I believe tommy d could fill you in on a lot of local horror stories. 

Sent from my iPhone

On Jun 3, 2013, at 10:24 AM, "Todd - Work" <t...@fpdc.com> wrote:

> What exactly is the purpose of a forward flow test on a backflow preventer? 
> This is not required on other check valve devices such as alarm valves, riser 
> checks, water meters, etc. Has there been a history of problems that this 
> seems to solve? 
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 
> On Jun 3, 2013, at 10:03 AM, <rfletc...@aerofire.com> wrote:
> 
>> NFPA 13 and 24 only require the forward flow test. Maybe they could be 
>> changed to require a "means" to forward flow test? Around here most BFP's 
>> are installed at the property line so they are not in the FP contractor's 
>> scope.
>> 
>> Ron F 
>> 
>> -----Original Message-----
>> From: sprinklerforum-boun...@lists.firesprinkler.org 
>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mark A. 
>> Sornsin, P.E.
>> Sent: Monday, June 03, 2013 6:13 AM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: RE: test header
>> 
>> Moreover, the engineer could specify Ron's solution up front. Doesn't help 
>> the design-build jobs - but you as the contractor could offer it up 
>> front...in such a way that makes you look like you're helping the customer, 
>> not just seeking a means to get more money out of them (easy to say...).
>> 
>> I've been asked why we spec these test outlets on our jobs.  When I ask the 
>> contractor how they do their annual full-flow testing thought the backflow 
>> assemblies, they answer with a description like we've discussed here - 
>> except that it is clear that they are answering a theoretical situation - 
>> they normally aren't doing the forward flow testing of the backflow 
>> assemblies - neither at the end of a job, nor during their annual testing.
>> 
>> 
>> Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection 
>> Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
>> http://www.kfiengineers.com
>> 
>> -----Original Message-----
>> From: sprinklerforum-boun...@lists.firesprinkler.org 
>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ron 
>> Greenman
>> Sent: Friday, May 31, 2013 2:41 PM
>> To: sprinklerforum@lists.firesprinkler.org
>> Subject: Re: test header
>> 
>> By the time toy've drained the system, removed the FDC and put in a spool, 
>> removed the FDc, done the flow, drained everything again, replaced all the 
>> parts, probably be compelled to do a hydro on the FDC line, and then are 
>> nearly due to do it again, you could have just put in a test header, or 
>> mech-teed a couple of fire hose valves onto the FDC line, or the riser 
>> quicker and for less money, and nobody has to go through that nonsense again.
>> 
>> 
>> On Fri, May 31, 2013 at 12:22 PM, G. Tim Stone <tston...@comcast.net> wrote:
>> 
>>> Take the flappers out or just remove the FDC fitting.
>>> 
>>> Regards,
>>> G. Tim Stone
>>> 
>>> G. Tim Stone Consulting, LLC
>>> NICET Level III Engineering Technician Fire Protection Sprinkler 
>>> Design and Consulting Services
>>> 
>>>               117 Old Stage Rd. - Essex Jct., VT. 05452
>>> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>>>                          tston...@comcast.net
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to