Whoops, forgot that to get to 1.09 for the required section modulus, you first have to divide PL by 4, then by 15,000. See how easy it is for even a smart aleck like me to make a mistake? The answer was correct, but the explanation was flawed, that's why my teachers always asked to show the work.

    65,696.4divided by 4= 16,421 and that divided by 15,000 = 1.094

Forgetting a step like that got me much lower grades.
*

PARSLEY CONSULTING

*

Ken Wagoner

760.745.6181 voice

760.745.0537 fax

website: www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>

On 6/3/2013 7:51 AM, ParsleyConsulting wrote:
Brad,
Part 1 - Gibberish. Pure and simple. The tables in NFPA 13 didn't reduce the "force" and "distance" by half in their calculations. It simply used the formula to calculate the maximum moment at the point of the load for a simple beam, based on the maximum length of various pipe sizes between hangers. That's why the figures for 1" and 1-1/4" are based on 12' between hangers. The maximum moment is the "worst case", and was what the committee saw as providing system designers with enough information to allow them to not use trapeze members which would have excessive loads placed on them. The formula to determine maximum moment is PL/4, with P=weight of pipe being supported in pounds (including 250#), and L=the length of the span of the trapeze in inches. The moment is then divided by the maximum allowable bending stress, which for steel is 15,000. The resulting equation looks like this: (PL/4)/15,000 = required section modulus. So, for 15' of 1-1/2" sch 40 pipe, the value of P would equal 15' x 3.61 = 54.15 + 250 = 304.15#. For an 18' span, the value of L = 216". Multiply PxL = 65,696.4, and then divide that value by 15,000, and the result is a required section modulus for the worst case location of the load (mid span) of 1.09 in³. That is just slightly less than doubling the value for a 9'-0" span, however using that method would result in a larger required section modulus, so it would work out in the end. The 4ab/a+b you reference is a method to calculate the equivalent length of the trapeze, in order to reduce the value of "L" in the original equation. Going back to your 18' span, if the load were 3' from one end, and 15' from the opposite end, that results in the equation 4x180x36/180+36, which equals 120", or 10'. The value of L in the above equation is changed from 216"to 120", reducing the required section modulus. PL/4 now becomes 304.15 x 120 = 36,498which is divided by 4, resulting in 9,124.5, which is further divided by the allowable bending stress of 15,000 for steel, with a final required section modulus of 0.6083 in³. Round that up to 0.61, and it matches the value in NFPA 13, Table 9.1.1.7.1(a) (2013).
No reduction by half anywhere in those equations.
Part 2 - Relatively correct regarding doubling the require section modulus for a 9' span, however as the structural engineers in the room when this table was expanded to include spans up to 16'-0" notedyou can keep increasing the span to the point where the weight of the trapeze itself now becomes an issue in the overall capacity to resist bending, and that sort of calculation was one they were reluctant to provide without a significant amount of additional information. Please note that this is my opinion only, and does not reflect that of the NFPA 13 Hanging and Bracing Committee.
*

PARSLEY CONSULTING

*

Ken Wagoner

760.745.6181 voice

760.745.0537 fax

website: www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>

On 5/31/2013 7:36 PM, Brad Casterline wrote:
saw an e-mail the other day about 18 foot trapeze spans.

wished someone had asked me.

i would have said---either:

section modulus is moment divided by stress. moment is half the force(lb)
times half the distance(in).

the force is the weight of the water-filled pipe plus 250. the distance is
4ab/a+b.

the stress is 15,000.

or: double the required section modulus for a nine foot span.


Brad Casterline, NICET IV

Fire Protection Division


FSC, Inc.

P: 913-722-3473

[email protected]

www.fsc-inc.com


Engineering Solutions for the Built Environment


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to