It was always the intent that you could not mix sprinkler types (since there 
has never been a stated means of combining different design basis).  The source 
of the problem was that the 2010 ed and earlier wording that was an archaic 
left-over when referring to the sprinkler as a fast response type (see 
8.4.5.3).  Thus some assumed that meant any type of fast response sprinkler so 
I guess an ESFR sprinkler would fit that bill.  The problem becomes apparent 
when attempting to mix the different design basis.

Roland

 
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX