It was always the intent that you could not mix sprinkler types (since there has never been a stated means of combining different design basis). The source of the problem was that the 2010 ed and earlier wording that was an archaic left-over when referring to the sprinkler as a fast response type (see 8.4.5.3). Thus some assumed that meant any type of fast response sprinkler so I guess an ESFR sprinkler would fit that bill. The problem becomes apparent when attempting to mix the different design basis.
Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Jun 6, 2013, at 6:38 PM, Pete Schwab <[email protected]> wrote: > The NFPA 13 committee has made it clear in the 2013 edition that you cannot > mix QR and Residential in the same compartment. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org