Without looking anything up I'm pretty sure that if the longitudinal flue space is not blocked and the shelves are less than 64 sqft. it's okay. You would have to look up the definition of solid shelves etc... but the info is in the book. I think FM is different than NFPA on shelves smaller than 64 sqft.
Ron F -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Brian Harris Sent: Thursday, June 13, 2013 12:18 PM To: [email protected] Subject: ESFR & Racks Quick question for all you storage pro's.... I know that one of the limitations of using an ESFR system where there is rack storage is that the shelves cannot be solid. I don't see anywhere that says what the shelves can be made out of and is there a percentage of "open" space that the shelves need to be to not be considered solid? Brian Harris, CET BVS Systems Inc. Sprinkler Division bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org