Looks like you're looking in 13D and not 13 w/ that code section.

According to NFPA 13 garages are an ordinary hazard group I occupancy.




On Thu, Jun 20, 2013 at 10:28 AM, Vince Sabolik <[email protected]> wrote:

> Good afternoon, forum --
>
> Using 13R applying to a 3 story condo....
>
> 7.3 Design Criteria — Garages.
> 7.3.1 Garages that are completely separated from the residential
> portion of the building by fire-resistive construction
> sufficient to have them considered separate buildings under
> the local code shall be protected in accordance with NFPA 13.
>
> OK, go to 13...
>
> 8.3.4* Sprinklers shall not be required in garages, open attached
> porches, carports, and similar structures.
>
> Are sprinklers required in the garage or not?
>
>
>
> Vince Sabolik, West Tech Fire Protection, Inc.
> 11351 Pearl Road / Strongsville, Ohio 44136       440 238-4800     Fax 440
> 238-4876
>
>