Looks like you're looking in 13D and not 13 w/ that code section. According to NFPA 13 garages are an ordinary hazard group I occupancy.
On Thu, Jun 20, 2013 at 10:28 AM, Vince Sabolik <[email protected]> wrote: > Good afternoon, forum -- > > Using 13R applying to a 3 story condo.... > > 7.3 Design Criteria — Garages. > 7.3.1 Garages that are completely separated from the residential > portion of the building by fire-resistive construction > sufficient to have them considered separate buildings under > the local code shall be protected in accordance with NFPA 13. > > OK, go to 13... > > 8.3.4* Sprinklers shall not be required in garages, open attached > porches, carports, and similar structures. > > Are sprinklers required in the garage or not? > > > > Vince Sabolik, West Tech Fire Protection, Inc. > 11351 Pearl Road / Strongsville, Ohio 44136 440 238-4800 Fax 440 > 238-4876 > > > ______________________________**_________________ > Sprinklerforum mailing list > Sprinklerforum@lists.**firesprinkler.org<[email protected]> > http://lists.firesprinkler.**org/listinfo.cgi/** > sprinklerforum-firesprinkler.**org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org> > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
