AHJs tend to try to worry property and firefighter protection into 13D.
Reasonable from their point of view, but the idea behind the standard is 1.
get everyone out and 2. make it cheap enough to b attractive to all the
naysayers. If the occupants escape and it burns to the ground no problem,
met the performance spec (everybody got out). If it's too dangerous for
firefighters to enter and people are inside then it failed. If it's
dangerous and everyone is out leave it be. Don't get on the roof. Don't
ventilate. Don't attempt a save. Surround and drown is the proper response.
adding sprinklers too unoccupied spaces like garages won't help with 1 and
will be detrimental to 2.


On Thu, Jun 20, 2013 at 2:05 PM, Cahill, Christopher
<[email protected]>wrote:

> Sure.  That kinda stuff (putting heads in garages where not required by
> the standard) is what makes residential sprinklers a harder fight.  I
> understand a local can do what they want.  And maybe/probably they are even
> right.  But we always get accused of scope and job creep costing the
> builders money.  Because you know they are kind folks and absorb these
> additional costs.
>
> Chris Cahill, PE*
> Senior Fire Protection Engineer, Aviation & Facilities Group
> Burns & McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
>
> Proud to be one of FORTUNE's 100 Best Companies to Work For
> *Registered in: MN
>
>
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Matsuda,
> Richard
> Sent: Thursday, June 20, 2013 2:56 PM
> To: [email protected]
> Subject: RE: Residential Garages, 13R & me.
>
> Let me add more fuel to this discussion.
>
> 13D allows omitting the sprinklers from the garages...regardless of
> size...and regardless of whether or not additional living space is built
> above the garage.
> Here in Texas, they built everything bigger...houses with 4 to 10 car
> garages...and 2 or 3-story houses with living areas above the garages...and
> 13D doesn't require sprinklers in these garages. Several jurisdictions in
> the area already require sprinklers in the garages whenever there are
> living space above.
>
> Anyone wish to comment?
> rick matsuda
> city of dallas
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> Roland Huggins
> Sent: Thursday, June 20, 2013 2:05 PM
> To: [email protected]
> Subject: Re: Residential Garages, 13R & me.
>
> The repeat what John alluded to:  13D is focused solely on life safety
> (although property protection typically comes along for the ride for MOST
> fires) as portrayed by the 10 minutes supply.  13R intends a longer
> duration of life safety and a small bump in property protection with the
> 30 minute supply and larger design area. IN looking at section 1.2.1 -
> Purpose for both documents, the term property protection is not in 13D but
> is in 13R.
>
> Roland
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
>
>
>
>
>
> On Jun 20, 2013, at 11:41 AM, Vince Sabolik <[email protected]> wrote:
>
> > At the risk of sounding even more stupid than I feel, why would 13D
> > allow ommission of garage heads and 13R not?
> >
> > Same situation, the garage is under a room (above) in 13D -or- in 13R,
> > just an extra story.
> >
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)