NFPA 25-2011

10.3.4.3.1.1   Where the nature of the protected property is such that water 
cannot be discharged, the nozzles shall be inspected
for proper orientation and the system tested with air to ensure that the 
nozzles are not obstructed.

10.3.4.3.2   Where obstructions occur, the piping and nozzles shall be cleaned 
and the system retested.

Larry Keeping, P.Eng.

Professional Loss Control
3413 Wolfedale Road, Suite 6
Mississauga, Ontario
L5C 1V8

Phone:   905-949-2755, ext. 204
Fax:        905-949-1752

E-mail:    [email protected]

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jim 
Davidson
Sent: June-21-13 4:45 PM
To: [email protected]
Subject: RE: air test for open head deluge system

Thank you for adding some laughter on Friday. 

NFPA 25 Paragraph 11.3.2.6 Discharge Patterns.   

11.3.2.6.1 The discharge patterns from all of the open spray devices shall be 
observed to ensure that patterns are not impeded by plugged discharge devices 
and to ensure that discharge devices are correctly positioned and that 
obstructions do not prevent discharge patterns from covering surfaces to be 
protected.

Requires the system to be flow tested annually, there is no air test in NFPA 25 
for a deluge foam water system. The word observed means to look at the water 
discharge through the nozzle the wording "discharge patterns from all of the 
open spray devices shall be observed to ensure that patterns are not impeded" 
is the criteria needing to be review which means water of water/foam solution. 

Have a fire safe day.

Regards

Jim   


DAVIDSON ASSOCIATES

Fire Protection Engineering     P. O. Box 4010
Code Consultants        Greenville, DE  19807-0010
Medical Gas Systems Engineering (302) 994-9500
        Fax (302) 234-1781

CONFIDENTIALITY
This report and any attachments are confidential and also may be privileged.
If you are not the named recipient, or have otherwise received this report in 
error, please destroy the report, notify the sender immediately, and do not 
disclose its contents to any other person, use them for any purpose, or store 
or copy them in any medium.
Thank you for your cooperation.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Friday, June 21, 2013 4:31 PM
To: [email protected]
Subject: Re: air test for open head deluge system

Best laugh I've had all day. 

Thank you, Brad. 

bv 

----- Original Message -----
From: "Brad Casterline" <[email protected]>
To: [email protected]
Sent: Friday, June 21, 2013 12:59:17 PM
Subject: RE: air test for open head deluge system 

maybe they hare test-- the one where you check for rabbits in the bladder tank? 

-----Original Message-----
From: John Denhardt [mailto:[email protected]]
Sent: Friday, June 21, 2013 2:51 PM
To: [email protected]
Subject: Re: air test for open head deluge system 

Agree. Something is off. 

Sent from my Motorola Smartphone on the Now Network from Sprint! 


-----Original message-----
From: Ron Greenman <[email protected]>
To: "[email protected]" 
<[email protected]>
Sent: Fri, Jun 21, 2013 15:46:42 EDT
Subject: Re: air test for open head deluge system 

These questions intrigue me because it's about what might be an arcane 
application. What I found was that an open head deluge system is essentially 
just a type of sprinkle system in 25 and so tested the same as any other. When 
it starts being defined is something having to do with a special application 
(water-spray, foam, etc.) then there are additional operational tests. So when 
you look at deluge it sends you various places within 25. One took me the ultra 
high speed stuff.
Another to water spray. 
And yes there is one for foam and it sent me to the foam section for plain old 
sprinkler systems. In no case did I run into the air test tree while wandering 
around the NFPA 25 forest. Have your client ask this other guy for the 
reference that says this is a test, much less a mandatory one. 
Maybe he was saying he needs to test the air compressor...oh,..wait..., open 
head system?...Air compressor?...Something isn't making sense. 


On Fri, Jun 21, 2013 at 12:04 PM, Martinez, Dewayne < 
[email protected]> wrote: 

> I have a owner calling me because another contractor is stating that 
> he needs to have an air test done on his open head foam deluge system.
> 
> I have never heard of this and was wondering what the test entails. 
> Any takers? 
> 
> Thanks,
> 
> 
> 
> Dewayne Martinez
> 
> Fire Protection Design Manager
> 
> Total Mechanical
> 
> 414-406-5208 (c) 262-522-7110 (w) 262-522-1006 (f)
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> 
> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org 
> 



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave. 
Tacoma, WA 98405 

[email protected] 

http://www.bates.ctc.edu/fireprotection/ 

253.680.7346
253.576.9700 (cell) 

Member: 
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC 

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to