We a forward flow at a church last week.  When we did the  main drain flow test 
we got 30 PSI.   We tested through a single snoot FDC, with the FDC check valve 
turned around, the clapper valve was not removed. 
#1  forward flow test with 1.5” nozzle.  We got 24 PSI, 337 GPM
#2 forward flow test with 2” nozzle, 16 PSI and 493 GPM
# 3 forward flow test with 2.25” nozzle, 12 PSI and 536 GPM
The above results were with a straight fixed nozzle

The hydraulic name plate 
Design Density .10 GPM
Area of operation 917 Sq Ft (the sprinkler protects the basement, which houses 
a day care, 2 bathrooms, janitor closet, mechanical room, elevator room, and a 
hallway. 
System demand at bottom of riser 242.8 GPM at 59.95 PSI
Water supply flow test, 84 PSI static, 70 PSI residual flowing 981 GPM


The water flow comes through the wall, 6 inches off the floor, makes a 90°, up 
through the backflow device, through the 2.5 inch alarm check valve, 3 more 90° 
to the single snoot FDC. Then through the wall and our flow tester.  The water 
was clean after 1 minute.  We did not do a comparison with a certified gauge, 
nor did we replace the gauges on the wet pipe. 

The chart is supplied with the flow tester. 

Do these results look legitimate?  A larger nozzle = more GPM and less PSI?