Maybe I missed this, but the study, testing and report surprisingly does not 
acknowledge or mention the fact that many if not most cloud ceiling conditions 
are where the the ceiling above the clouds is the structural deck supported by 
beams and girders.

That structure can divide the above ceiling surface into compartments that can 
either hold or channel away combustion products from the gaps. The structural 
members above cloud ceilings are more likely to be deeper than normal because 
clouds are often architectural methods used to break up the ceiling expanse 
resulting from wide structural bays where the architecture wants to eliminate 
columns. A cloud ceiling in a small room, i.e. where the structure above might 
be less involved, may not be architecturally appealing and may be there as a 
primary result of a not so common HVAC concept.          

The test apparatus was in fact one reused from testing the effects of 
structural steel. They can put that steel back up and run the cloud tests again 
under more likely conditions to see how far the no steel conclusions can carry.

Allan Seidel
St. Louis, MO


On Aug 8, 2013, at 9:18 AM, Brad Casterline <[email protected]> wrote:

> http://www.nfpa.org/research/fire-protection-research-foundation/reports-and
> -proceedings/suppression/other-sprinkler-protection/sprinkler-protection-for
> -cloud-ceilings
> 
> 
> 
> Brad Casterline, NICET IV
> 
> Fire Protection Division
> 
> 
> 
> FSC, Inc.
> 
> P: 913-722-3473
> 
> [email protected]
> 
> www.fsc-inc.com
> 
> 
> 
> Engineering Solutions for the Built Environment
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to