Extended coverage dry heads do have different K-factors depending on the
length.  See the Tyco DS-2, for example.


Benjamin Young


On Thu, Aug 15, 2013 at 11:13 AM, Roland Huggins <[email protected]
> wrote:

> Ahh but we are intermixing reality and assigned methodology.  With all the
> averaging to define the K-factor, applying rectangles to circular discharge
> patterns, differences in losses in fittings, etc etc etc despite using a
> very precise calculation equation, we still are making a rough estimate
> that works very well at ensuring fire control.
>
> Just like the cut-sheet shows, the nominal K-factor is used.
>
> Roland
>
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
>
>
>
>
>
> On Aug 15, 2013, at 6:47 AM, Steve Leyton <[email protected]>
> wrote:
>
> > I would check with the manufacturer of the specific sprinkler you are
> proposing to install.  Dry sprinklers have internal moving parts and the
> designs aren't necessarily the same between different ones; if there's a
> measurable added friction loss in the barrel from flow over and through the
> various tube and spring assemblies, I'd wager they've got the net K or
> pressure loss available.
> >
> > Steve Leyton
>