High piled double row rack storage with in-rack sprinklers.  Per design 
selected (FM) longitudinal flue heads at every upright and not to exceed 10' 
o.c.  This is a design that allows one not to consider the overhead sprinklers. 
 Long story but seemingly the best approach for a reconverted hangar from the 
1950's with unknown deluge design.

Cantilever racks with uprights (columns) variable at 2'-8' spacing.  Of course 
the uprights are more like 18" steel columns with 6" flanges.  Does one put a 
head at every upright? Down to 2' o.c. seems a little ridiculous?  No matter 
where you put the head there is a large shadow on the other side of the 
rack/column.  I believe NFPA says locate heads 3" from upright but I think they 
are talking about the little few inch wide typical rack design not cantilever 
columns. Thought about solving that problem with a row down each side of the 
upright but then stuck with the every upright or 10' o.c.  Anyone done a 
cantilever with in-racks lately?

Chris Cahill, PE*
Senior Fire Protection Engineer
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]<mailto:[email protected]>
www.burnsmcd.com<http://www.burnsmcd.com/>

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN