6.2.1.1 (2013) When a sprinkler has been removed for any reason, it shall not be reinstalled.
Handbook: Because of concerns that sprinklers could be damaged during the removal process, this requirement was added to the 2013 edition to clarify that when a sprinkler is removed from the piping it is to be replaced with a new sprinkler. When a sprinkler is removed, damage could occur to the water seal and operating element, specifically a glass bulb type element, which could impact sprinkler performance without any visual indication. Duane Johnson, PE Program Manager Division of the Fire Marshal (Contractor) Office of Research Services National Institutes of Health 301-496-0487 "Protecting Science - One Sprinkler at a Time" -----Original Message----- From: Thomas Watt [mailto:[email protected]] Sent: Thursday, September 05, 2013 10:28 AM To: [email protected] Subject: Re: removing sprinkler on drop Im with Greg. I have reinstalled thousands of heads without issue. What is the justification for this requirement? On Thursday, September 5, 2013, Greg McGahan <[email protected]> wrote: > its ALL ridiculous if you ask me.... > it is a waste of resources > > > On Thu, Sep 5, 2013 at 7:53 AM, Brad Casterline ><[email protected] >wrote: > >> There is wording somewhere that supports NOT... >> >> -----Original Message----- >> From: Todd - Work [mailto:[email protected]] >> Sent: Thursday, September 05, 2013 7:48 AM >> To: [email protected] >> Subject: removing sprinkler on drop >> >> I am working on a project where we have to add heads above an >> existing ceiling on an existing system. The pendant heads are fed on swing >> joints. >> My >> plan is to have them removes the drops (with sprinkler in them) >> replace the >> 1" elbow with a tee and re-install the drops. The question came up >> about replacing the pendant heads. They were not removed from the >> pipe but the pipe with head was removed from the system. I never >> thought about this before and can see arguments on both sides. Replace the >> pendants or not? >> >> Todd G Williams, PE >> Fire Protection Design/Consulting >> Stonington, CT >> www.fpdc.com >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >> > > > > -- > Greg McGahan > Living Water Fire Protection, LLC <http://www.livingwaterfp.com> > 1160 McKenzie Road > Cantonment, FL 32533 > 850-937-1850 > fax 850-937-1852 > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org