Exactly - you are basically calculating a demand flow & pressure back to the 
fire pump discharge.  If for instance that demand is 50 PSI at 750 GPM, as long 
as that "demand" is under your combined city/fire pump curve then you can use 
the minimize test header pipe size as indicated in NFPA 20. 

Jeffrey J. McNall
Fire Sprinkler Division Manager
Access Fire
28 Mill Street
Tilbury, ON N0P2P0
Mobile: 519-777-8520
*Please note new email address [email protected]

-----Original Message-----
From: James D. Waite [mailto:[email protected]] 
Sent: September-19-13 11:34 AM
To: [email protected]
Subject: RE: Fire Pump Test Header Calculation

I like the analogy.

To make sure we're on the same page, if I require a pitot pressure of 10 psi at 
my hose monster, and I lose 60 psi back to the pump discharge.  If the pump 
discharge gauge shows 100 psi, my test header line would be adequately sized 
(under the curve). Correct?

Jimmy Waite, CET - Design Manager
Fire & Life Safety America- Raleigh District
7711 Welborn Street, Suite 103
Raleigh, NC  27615
Office: 919-872-3250
Cell: 919-868-3546
Fax: 919-877-5775
www.flsamerica.com




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brad 
Casterline
Sent: Thursday, September 19, 2013 11:16 AM
To: [email protected]
Subject: RE: Fire Pump Test Header Calculation

I would look at it like this: The discharge gage is like the flow test hydrant 
that you are calcing to. The test header is like the remote area with a PSI and 
GPM demand, and the test header pipe, fittings, and hose is between the two 
points. The pitot gage reading at the test header is measuring the velocity 
pressure so the velocity can be determined in ft/sec, times square feet nozzle 
area (times .97), to give ft3/sec, or GPM.

-----Original Message-----
From: James D. Waite [mailto:[email protected]]
Sent: Thursday, September 19, 2013 9:47 AM
To: [email protected]
Subject: RE: Fire Pump Test Header Calculation

Right.  So the worksheet from NFPA 20 basically calculates a total amount of 
friction loss from the pump to the pitot.

So, my discharge gauge shows the total of the pump pressure and the city 
supply.  I use the worksheet to calculate a total friction loss.  Would the 
total calculated friction loss have to be less than the reading on the 
discharge gauge? Or, would the friction loss have to be less than the discharge 
gauge reading minus the pump's added pressure (i.e. the city supply)?

How does this calculation relate to the flow being measured?  Or are the two 
unrelated?


Jimmy Waite, CET - Design Manager
Fire & Life Safety America- Raleigh District
7711 Welborn Street, Suite 103
Raleigh, NC  27615
Office: 919-872-3250
Cell: 919-868-3546
Fax: 919-877-5775
www.flsamerica.com



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad 
Casterline
Sent: Thursday, September 19, 2013 6:17 AM
To: [email protected]
Subject: RE: Fire Pump Test Header Calculation

Jimmy,

I would guess that if your pump discharge PSI at the 150% rated GPM test flow 
(from the pump curve) is higher that what you calculated for the required pump 
discharge, you have proved it-- (demand is 'under the curve'
using that pipe size).

-----Original Message-----
From: James D. Waite [mailto:[email protected]]
Sent: Wednesday, September 18, 2013 6:10 PM
To: [email protected]
Subject: Fire Pump Test Header Calculation

Can I get some assistance with a fire pump test header calculation?

I got the calculation form from 20:4.20.3.4, and I have it filled out.  But 
what to I do next?  How do I use it to confirm the pipe size?


Jimmy Waite, CET - Design Manager
Fire & Life Safety America- Raleigh District
7711 Welborn Street, Suite 103
Raleigh, NC  27615
Office: 919-872-3250
Cell: 919-868-3546
Fax: 919-877-5775
www.flsamerica.com<https://owa.flsamerica.com/owa/www.flsamerica.com>


________________________________

The information contained in this email and any attached documents may contain 
information that is the confidential property of Fire & Life Safety America, 
Inc ("FLSA"). Any documents created on any FLSA computer or by any employee in 
the conduct of FLSA business is work product and owned by FLSA.
If the reader of this message is not the intended recipient, or the employee or 
agent responsible to deliver it to the intended recipient, you are hereby 
notified that any dissemination, distribution or other use of the contents of 
this communication is strictly prohibited. If you have this communication in 
error, please immediately notify the sender and delete this email.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

________________________________

The information contained in this email and any attached documents may contain 
information that is the confidential property of Fire & Life Safety America, 
Inc ("FLSA"). Any documents created on any FLSA computer or by any employee in 
the conduct of FLSA business is work product and owned by FLSA.
If the reader of this message is not the intended recipient, or the employee or 
agent responsible to deliver it to the intended recipient, you are hereby 
notified that any dissemination, distribution or other use of the contents of 
this communication is strictly prohibited. If you have this communication in 
error, please immediately notify the sender and delete this email.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

________________________________

The information contained in this email and any attached documents may contain 
information that is the confidential property of Fire & Life Safety America, 
Inc ("FLSA"). Any documents created on any FLSA computer or by any employee in 
the conduct of FLSA business is work product and owned by FLSA. If the reader 
of this message is not the intended recipient, or the employee or agent 
responsible to deliver it to the intended recipient, you are hereby notified 
that any dissemination, distribution or other use of the contents of this 
communication is strictly prohibited. If you have this communication in error, 
please immediately notify the sender and delete this email.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to