Steve,

Section 506.6 of the Mechanical Code requires sprinklers inside ducts exceeding 
10-inches that convey flammable vapors or fumes, but I cannot find a similar 
mandate for ducts conveying sawdust in either NFPA 664, CBC or CFC.

Interestingly, NFPA 664 speaks about duct sprinklers free of debris "where 
provided", but there is no mandate to actually provide duct protection. I used 
to work for a large aerospace firm and I don't recall any of the ducts having 
sprinklers, except those that conveyed flammable vapors. 

Galen Taylor
County of Los Angeles Fire Department
Fire Prevention Engineering
323-890-4339
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve 
Leyton
Sent: Thursday, September 19, 2013 9:33 AM
To: [email protected]
Subject: Dust collection - where/when are sprinklers required

I have looked through the California editions of International Fire Code and 
Building Code and cannot find any prescriptives for sprinklers in
dust collection systems in woodworking facilities.   Does anyone know
where the triggers are published, if anywhere?  Is it in NFPA 664?

 

Steve Leyton

PROTECTION DESIGN & CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-------------------------------------------------------------

Ph:      858.751.2930 - ext. 102

Fax:    858.751.2933

Cell:  619.972.5696

 

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to