Its not telling you to install 50 ft. of pipe from the suction flange but it is saying that you can only install a listed OS&Y valve within 50 ft of the suction flange.
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jeremy Frazier Sent: Wednesday, October 02, 2013 11:52 AM To: [email protected] Subject: NFPA 20 (2010) 4.27.3.1 BFp to be installed 50' from the fire pump suction flange (as measured along the route of the pipe). Is this a typo? What it the reasoning for having such a long run of pipe without valves? In a small fire pump room with a bfp, It would seem you would have to do a bunch of zig zags with the pipe just to meet this requirement. Jeremy Frazier Designer Cavalier Fire Protection P:571-931-1004 F:571-931-1010 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ------------------------------------------------------------------------------ This e-mail contains information that may be privileged and/or confidential. If you are not the intended recipient, any disclosure, distribution, copying or other use of this e-mail or the information contained herein or attached hereto is strictly prohibited and may be unlawful. If you have received this e-mail in error, please notify this sender immediately and delete this e-mail without reading, printing, copying or forwarding it to anyone. Thank you for your co-operation. ------------------------------------------------------------------------------ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org