>From my 1961 Edition:

(in bold print no less)

1421. Sprinkler system layout and installation should be entrusted to none
but fully experienced and responsible parties. Sprinkler system
installation is a trade in itself. Inspectors cannot be expected to act as
working superintendents or correct errors.


David Autry

Meininger Fire Protection Inc.
2521 W L St. Suite No.4
Lincoln, Ne 68522
Voice (402) 466-2616
Fax (402) 466-2617
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Cahill, Christopher
Sent: Wednesday, October 09, 2013 10:37 AM
To: [email protected]
Subject: RE: Sprinklers Below Overhead Doors

I wish I could find my 1936 copy.  That was in there.  Well it went more
like this...sprinklers are their own trade and shall be installed by only
those trained and experienced.  AHJ is not a field superintendent and is
not expected to supervise the work.  OK maybe yours improves with bringing
AHJ into the knowledgeable.

Chris Cahill, PE*
Senior Fire Protection Engineer
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered
in: MN




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, October 09, 2013 10:31 AM
To: [email protected]
Subject: RE: Sprinklers Below Overhead Doors

As I have remarked before. 1.2.2 ('13) should be amended to "shall require
knowledgeable and experienced design, installation, plan review and
enforcement".
Ron F

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Steven Scandaliato
Sent: Tuesday, October 08, 2013 8:17 PM
To: [email protected]
Subject: RE: Sprinklers Below Overhead Doors

Dwight y et al,
I was waiting for someone to finally bring up this section...everyone
needs to stop and read this section.  How many of you actually knew this
was in here?  That's right....someone actually requested a formal
interpretation regarding the need for sprinklers under conference tables
because why???
They are over 48"!  Are you kidding me?  The first time I read that back
in the early 80's I thought long and hard about getting back into beach
bartending.  I would LOVE to dive head first into this subject....but
maybe
6 people would care and the rest would lose interest after the first 6
pages.....As ridiculous as 8.5.5.3.2 sounds, it originated as a response
to a formal interpretation back in the late 70's.  How it found its way
into the actual body of the text is because it was a formal
interpretation...cause God knows none of us would ask such a
question....right?

Actually is wasn't the question that killed me, it was the answer.
Instead of saying something like, "no,  let's not get carried away" or "no
cause we don't think there will ever be enough trash or ignition sources
under conference tables" they (the committee) came back with "no because
its not
fixed"!  AAAAHHH!  Are you kidding me?   I haven't seen to many conference
tables that need to be bolted to the floor to call them fixed, but
nevertheless there it is...meaning, we are going to start putting
sprig-ups under conference room tables if they are determined to be
"fixed"!

 So is it an exception or just something that gives us a false sense of
understanding.  For example, because a duct that is 49" wide  and is
obviously considered "fixed" requires a sprinkler,  the fact that it is
only 24" off the floor in a mechanical room changes things?  This rule is
my favorite rule...and I could pontificate for hours...I need to settle
down and go get a glass of red....  For now, I think the appendix for
8.5.5.3.1 gets us out of this one (overhead doors) and we can move onto
something else....unless of course you'd like to read 25 pages (not
including
illustrations) of Sicilian rhetoric regarding the "Obstruction Rules for
Sprinklers; Life With the 4 Foot Rule"....LOL!  Surely we all have better
things to do...like read the new phone book!
Ciao,

Steven Scandaliato, SET CFPS
520.971.2322 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Dwight Havens
Sent: Tuesday, October 08, 2013 8:24 PM
To: [email protected]
Subject: Re: Sprinklers Below Overhead Doors

But wait...8.5.5.3.1 only applies to fixed obstructions over 4 foot
wide...8.5.5.3.2 provides an exemption for obstructions that are not
fixed, such as roll-up doors.

Dwight




________________________________
 From: Steven Scandaliato <[email protected]>
To: [email protected]
Sent: Monday, October 7, 2013 1:30 PM
Subject: RE: Sprinklers Below Overhead Doors


Wow...just a second....so how big does an obstruction have to be before it
will affect the operation?  There's only a handful of guys that I would
classify knowledgeable enough to speculate such a statement. That's a
pretty bold statement to make especially given the number of factors in
play including and most importantly ceiling height above the opened
door...

Let's step back a minute...we have a 4ft rule that has been around since
parchment paper and we have all swallowed the idea that as long as
something isn't greater than 48" we are all safe, but at 49" people may
die and buildings may burn down.  Agree or disagree with this untested
rule...it is what it is.  Now, unknown to many, we now have some modeling
and testing that is currently being worked over in this cycle to introduce
guidance for clouds and gaps.  However, until such time as that gets
worked over and argued about in committee, let's just stick with the 48"
rule and leave it at that...anything beyond that is pure beer and
peanuts.  Let's just say sprinklers are required under the doors and yes,
you can omit them.
23.4.4.6.3.1 and 2.  Hopefully we will have better info next edition.

Steven Scandaliato, SET CFPS
520.971.2322 Cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tony
Silva
Sent: Monday, October 07, 2013 11:06 AM
To: [email protected]
Subject: Re: Sprinklers Below Overhead Doors

Your question leads me to believe that you think only one head will
operate if the door was up. I don't believe the door will act as a heat
collector to prevent the head at the ceiling from operating. True, the
door when raised will be an obstruction but the door being up or down
won't have much of an effect on the operation of the sprinkler heads. So
why make a difference in the method of calculation?

Tony

----- Original Message -----
From: "Mike Hill" <[email protected]>
To: [email protected]
Sent: Monday, October 7, 2013 10:32:47 AM
Subject: Sprinklers Below Overhead Doors

Question: Are sprinklers below overhead doors required to be included in
hydraulic calculations?

When I first started in the industry, I was told that heads below overhead
doors were required to be included in the hydraulic calculations. The
reason being, it was a temporary obstruction. The door could be up or down
if a fire broke out, unlike a large duct which was a permanent
obstruction.

I was recently questioned by a FPE as to why I included heads below the
door in a hydraulic calculation. I explained my reasoning to him and he
accepted it. In his eyes I had proven a more demanding situation than was
needed so it didn't affect his stamping the plans. Flash forward a few
weeks and to a different project. I now have a much larger operating area
and removing these (11) heads from the calculation would help it greatly.
I am providing protection for a firehouse expansion on a military base.
This calculation is in the apparatus bay. UFC requirements are in effect,
ceiling height over 20'-0" and it is sloped enough to require the 30%
increase. The majority of the piping being calculated is existing and to
remain as is (if at all possible).

Using 2007 Edition of NFPA-13 (only one I have handy at the moment).
8.5.5.3.1 Specifically mentions overhead doors need protection below. No
problem here.

22.2.2.6.3 Does not mention overhead doors when providing situations where
sprinklers can be omitted from hydraulic calculations.

The wording in these sections seems to support what my mentors instilled
in my soft pliable mind all those years ago.

What says the forum?

Mike Hill



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to