Arm over is defined as pipe supplying a single head - if I remember correctly. 
Restraint is not required for arm overs. So technically not required. 

Travis Mack, SET
MFP Design, LLC

Sent from my iPhone

> On Oct 20, 2013, at 6:01 PM, "Cahill, Christopher" <[email protected]> 
> wrote:
> 
> Issue is not about vertical restraint from >100 psi. Well below. This is 
> strictly an EQ question. 
> 
> 
> Chris Cahill, PE*
> Senior Fire Protection Engineer 
> Burns & McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
> 
> Proud to be one of FORTUNE's 100 Best Companies to Work For
> *Registered in: MN
> 
> 
> 
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Dwight 
> Havens
> Sent: Sunday, October 20, 2013 6:13 PM
> To: [email protected]
> Subject: Re: NFPA 13 '10 9.3.6 BL Restraint
> 
> pendent heads w/ > 100 psi
> 
> 
> 
> 
> 
> 
> On Sunday, October 20, 2013 6:44 PM, "[email protected]" 
> <[email protected]> wrote:
> 
> Isn't the thrust restraint a requirement for systems with pressures in excess 
> of 100 psi?
> 
> ----- Original Message -----
> From: Ron Greenman [mailto:[email protected]]
> Sent: Sunday, October 20, 2013 09:42 PM
> To: [email protected] 
> <[email protected]>
> Subject: Re: NFPA 13 '10 9.3.6 BL Restraint
> 
> Don't have anything at the moment. Is this eq country? Somewhere there's 
> something that requires up thrust restraint at the end of line. I think 
> lateral is only required for seismic areas, but I'd need to read the section 
> before I made an unequivocal statement. No books in the car. 
> 
> Sent from my iPhone
> 
>> On Oct 20, 2013, at 2:08 PM, "Cahill, Christopher" <[email protected]> 
>> wrote:
>> 
>> Got a code section that connects a length of a BL to a restraint or the 
>> inverse of what you said, that if it needs a hanger then it needs restraint? 
>>  I got one that says it doesn't, 9.3.6.7 Drops and armovers shall not 
>> require restraint. 3.5.3 Arm-Over. A horizontal pipe that extends from the 
>> branch line to a single sprinkler or a sprinkler above and below a ceiling. 
>> I just find it odd I can have a 2" pipe 100' long serving one head and it 
>> doesn't need anything but regular old gravity hangers.  Or I can't find 
>> anything to challenge 9.3.6.7.  My case I have a bunch of 3-8'  1" legit 
>> armovers.  Contractor didn't install restraint and I think he's right 
>> technically. 
>> 
>> Chris Cahill, PE*
>> Senior Fire Protection Engineer
>> Burns & McDonnell
>> 8201 Norman Center Drive
>> Bloomington, MN 55437
>> Phone:  952.656.3652
>> Fax:  952.229.2923
>> [email protected]
>> www.burnsmcd.com
>> 
>> Proud to be one of FORTUNE's 100 Best Companies to Work For 
>> *Registered in: MN
>> 
>> 
>> 
>> 
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of 
>> rongreenman .
>> Sent: Sunday, October 20, 2013 2:19 PM
>> To: [email protected]
>> Subject: Re: NFPA 13 '10 9.3.6 BL Restraint
>> 
>> Restraint is to avoid upward thrust and side to side thrust, whipping 
>> for Devo fans, at the end of a branch line. If an armover does not 
>> need a  hanger it wouldn't need restraint
>> 
>> 
>> On Sun, Oct 20, 2013 at 7:50 AM, Cahill, Christopher
>> <[email protected]>wrote:
>> 
>>> Two questions.
>>> 
>>> Is there a length of an armover that needs restraint?  Imagine a 12'
>>> armover that only feeds one head.
>>> 
>>> Can restraint be connected to something other than structure, like a 
>>> concrete floor above?
>>> 
>>> Chris Cahill, PE*
>>> Senior Fire Protection Engineer
>>> Burns & McDonnell
>>> 8201 Norman Center Drive
>>> Bloomington, MN 55437
>>> Phone:  952.656.3652
>>> Fax:  952.229.2923
>>> [email protected]<mailto:[email protected]>
>>> www.burnsmcd.com<http://www.burnsmcd.com/>
>>> 
>>> Proud to be one of FORTUNE's 100 Best Companies to Work For 
>>> *Registered in: MN
>>> 
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>> l
>>> er.org
>> 
>> 
>> 
>> --
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering Technology Bates Technical College
>> 1101 So. Yakima Ave.
>> Tacoma, WA 98405
>> 
>> [email protected]
>> 
>> http://www.bates.ctc.edu/fireprotection/
>> 
>> 253.680.7346
>> 253.576.9700 (cell)
>> 
>> Member:
>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>> 
>> They are happy men whose natures sort with their vocations. -Francis 
>> Bacon, essayist, philosopher, and statesman (1561-1626) 
>> _______________________________________________
> 
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to