Would it be helpful to swap out whatever type of pendents are in place now and 
install either institutional or concealed heads as a way of preventing damage.  
I have some seen some heated tempers in the locker room after some of my men’s 
league games and high school games that I have coached, but I have also not 
heard of this being a big problem either.

 

~Jarron

 

Jarron J. Gass, P.E. - Vice President - J. & J. Fire Protection Co., Inc.

101 Powell Rd., Butler, PA 16002, (724) 586-6111, fax (724) 586-5151

emergency (724) 898-2481,  <mailto:[email protected]> 
[email protected],  <http://www.jandjfire.com/> www.jandjfire.com 

 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of John 
Drucker - Home
Sent: Tuesday, November 05, 2013 12:05 PM
To: [email protected]
Subject: RE: Head Guards

 

Pay particular attention to 1.5.1.

 

NFPA-13

 

1.5 Equivalency. Nothing in this standard is intended to prevent the use of 
systems, methods, or devices of equivalent or superior quality, strength, fire 
resistance, effectiveness, durability, and safety over those prescribed by this 
standard.

 

1.5.1 Technical documentation shall be submitted to the authority having 
jurisdiction to demonstrate equivalency.

 

1.5.2 The system, method, or device shall be approved for the intended purpose 
by the authority having jurisdiction.

 

John Drucker, CET

Fire Protection Subcode Official

Fire / Building / Electrical Inspector

New Jersey

 

 

-----Original Message-----

From:  <mailto:[email protected]> 
[email protected] [ 
<mailto:[email protected]> 
mailto:[email protected]] On Behalf Of Forest 
Wilson Fire Sprinkler Comtractor

Sent: Tuesday, November 5, 2013 11:49 AM

To:  <mailto:[email protected]> 
[email protected]

Subject: RE: Head Guards

 

The best practice would be to submit the product sheets to the AHJ and ask for 
a variance to install the head guards. If he attaches them to the plywood then 
that's part of the ceiling and not part of the head though. And that affects 
the 18" clearance rule. 

 

 

Sent from my Galaxy S®III

 

-------- Original message --------

From: Gregory Lindholm < <mailto:[email protected]> [email protected]>

Date: 11/05/2013  11:33 AM  (GMT-05:00)

To:  <mailto:[email protected]> 
[email protected]

Subject: RE: Head Guards 

 

Yes John, that is the way I remembered it.

Thanks

 

> From:  <mailto:[email protected]> [email protected]

> To:  <mailto:[email protected]> 
> [email protected]

> Subject: RE: Head Guards

> Date: Tue, 5 Nov 2013 16:07:34 +0000

> 

> My educated guess is that there are no listed sprinkler guards for 
> semi-recessed sprinklers.  NFPA 13 requires the guard to be listed with the 
> specific sprinkler.

> 

> Bottom line - not available if you want to comply with NFPA 13.

> 

> John August Denhardt, P.E., FSFPE

> Strickland Fire Protection Incorporated

> 5113 Berwyn Road

> College Park, Maryland 20740

> Office Telephone Number:  301-474-1136 Mobile Telephone Number:  

> 301-343-1457 FIRE SPRINKLERS SAVE LIVES - Can you live without them?

> 

> 

> -----Original Message-----

> From:  <mailto:[email protected]> 
> [email protected] 

> [ <mailto:[email protected]> 
> mailto:[email protected]] On Behalf Of 

> Jamey Prentice

> Sent: Tuesday, November 05, 2013 11:02 AM

> To:  <mailto:[email protected]> 
> [email protected]

> Subject: Re: Head Guards

> 

> FPPI no idea on listing though

> 

> From: Gregory Lindholm

> Sent: Tuesday, November 5, 2013 10:58 AM

> To: SprinklerFORUM

> Reply To:  <mailto:[email protected]> 
> [email protected]

> Subject: Head Guards

> 

> 

> I think that this was discussed before, but are there any head guards 
> available for semi-recessed heads?

> I do not think that there are, but I have a customer that is looking 

> for even something that he could screw to the plywood ceiling that the 

> heads are coming through. (This is in an ice arena locker room.) Greg 

> Lindholm _______________________________________________

> Sprinklerforum mailing list

>  <mailto:[email protected]> 
> [email protected]

>  <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl> 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl

> er.org _______________________________________________

> Sprinklerforum mailing list

>  <mailto:[email protected]> 
> [email protected]

>  <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl> 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl

> er.org _______________________________________________

> Sprinklerforum mailing list

>  <mailto:[email protected]> 
> [email protected]

>  <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl> 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl

> er.org

     

_______________________________________________

Sprinklerforum mailing list

 <mailto:[email protected]> 
[email protected]

 <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________

Sprinklerforum mailing list

 <mailto:[email protected]> 
[email protected]

 <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

 

_______________________________________________

Sprinklerforum mailing list

 <mailto:[email protected]> 
[email protected]

 <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to