Why do you think you have plugs? Attic system or freezer?  

They usually form at the transition from warm to cold.  Should be within a few 
feet of that on the cold side.   And I'm sure per NFPA 13, pick your edition, 
been there a very long time.  
7.9.2* Spaces Maintained at Temperatures Below 32°F (0°C).
7.9.2.1 General.
7.9.2.1.1 Where sprinkler pipe passes through a wall or floor into the 
refrigerated space, a section of pipe arranged for removal shall be provided 
immediately inside the space.
7.9.2.1.2 The removable length of pipe required in 7.9.2.1.1shall be a minimum 
of 30 in. (762 mm).  

Chris Cahill, PE*
Senior Fire Protection Engineer 
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve 
Leyton
Sent: Monday, December 02, 2013 5:13 PM
To: [email protected]
Subject: Ice plug detection

Okay, slow day, I'll go first.   So ... who's got suggestions about how
to find ice plugs in existing systems without pulling everything apart or 
running a borescope down the piping?

 

Steve Leyton

PROTECTION DESIGN & CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-------------------------------------------------------------

Ph:      858.751.2930 - ext. 102

Fax:    858.751.2933

Cell:  619.972.5696

 

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to