Why can't the cross main in your case be called a 'branchline' since it
fits the description of one per the definition of '13: "The pipes supplying
sprinklers, either directly or through sprigs, drops, return bends, or
arm-overs." Then the 'armover' could magically become an.... armover.





On Wed, Jan 8, 2014 at 5:02 AM, Johnson, Duane (NIH/OD/ORS) [C] <
[email protected]> wrote:

> Based on the 2013 edition of 13, does a 1" pipe on a cross main feeding a
> single sprinkler require a restraint (ie. wire restraint)? Per 9.3.6.7,
> Drops and armovers shall not require restraint. Per the letter of the law,
> this pipe would be defined as a branchline...right? And therefore would
> require a restraint...right? Ok, what about when the 1" pipe is only 10"
> long? At this length, a hanger is not required, but what about the
> restraint?
>
> If the 1" pipe was 8' long, I can see the  need for a restraint, but for a
> short piece of pipe, does a restraint provide added benefit? For the
> purpose of restraints, is there a cutoff when the horizontal run should be
> reclassified as a branchline in lieu of an armover? At 2'? 6'? 10'?
>
> Help.
>
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Contractor)
> Office of Research Services
> National Institutes of Health
> 301-496-0487
>
> "Protecting Science - One Sprinkler at a Time"
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to