Sounds like a growing mushroom house.

On Wed, Jan 8, 2014 at 9:30 AM, Todd - Work <[email protected]> wrote:

> Each 40 ft x 64 ft room in this area has six 9 ft x 20 ft tables, spaced 1
> ft apart in one direction and 3 ft apart in the other. Agricultural
> occupancy so OH2 design. Tables are not skirted. In addition to wood
> construction, there will be plastic sheeting and plastic tubing under the
> table. (I am using the term "table" because that is what they call them).
> It will be a wet environment by nature of the occupancy.
>
> One interesting semantic note is that 11.2.3.1.8 (3), which is the 3000
> sqft requirement, references 8.14.6, which is the platform requirement also
> references combustible concealed spaces. But 8.14.6 only references
> combustible spaces. Nothing about them being concealed
>
> Looking at this from a practical perspective (think like fire), if a fire
> did start under a table, it could have significant time to develop before
> being detected. There may not be enough heat generated to activate a
> sprinkler until after it is well developed. Perhaps not until flames
> actually shoot up around the edge of the table. If flames shoot up around
> more than one side of the table (possible in a 9x20 table), then a lot of
> sprinklers over a fairly large area could open. More than would be included
> in a 1500 sqft area? Potentially. This is where my thought for the 3000
> sqft area comes from. (FWIW, EH2 occupancy description also references
> shielded fires).
>
> As for liability, the nature of our society is that we need to consider
> this as well as the technical aspect of our job.
>
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 860-535-2080 (ofc)
>
> > On Jan 8, 2014, at 11:23 AM, "Brad Casterline" <[email protected]>
> wrote:
> >
> > The distinction is probably not based on height.
> > By strict definition from an NFPA standard (other than 13) whichever you
> > call it and whether the sides are closed off or not it is not a concealed
> > space, so I vote* no on the 3000 S.F.
> > I think a 9" height is closer to a platform than a table so you have a
> > platform and if you do not put at least a screen 'skirt' around it to
> > prevent debris from accumulating underneath you will have to sprinkler
> under
> > it.
> >
> >
> > Brad
> >
> > *not a P.E. or A.H.J. so i vote :)
> >
> > -----Original Message-----
> > From: Todd - Work [mailto:[email protected]]
> > Sent: Wednesday, January 08, 2014 8:48 AM
> > To: [email protected]
> > Subject: Re: concealed space definition - part deux
> >
> > At what height does it cease to be a platform and become a table?
> >
> > If sprinklers are omitted from underneath the platform/table, would the
> > ceiling system need to be calculated to 3000 sqft?
> >
> > Todd G Williams, PE
> > Fire Protection Design/Consulting
> > Stonington, CT
> > www.fpdc.com
> > 860-535-2080 (ofc)
> >
> >>> On Jan 8, 2014, at 9:30 AM, "Brad Casterline" <[email protected]
> >
> >> wrote:
> >>
> >> NFPA 73-2006 3.3.6 (partial):
> >>
> >> Concealed:
> >> Rendered inaccessible by the structure or finish of the building.
> >>
> >> brad
> >>
> >> -----Original Message-----
> >> From: John Denhardt [mailto:[email protected]]
> >> Sent: Tuesday, January 07, 2014 4:56 PM
> >> To: <[email protected]>
> >> Subject: Re: concealed space definition
> >>
> >> I fully agree based on the 2013 edition.
> >>
> >> Thanks,
> >> John August Denhardt P.E.
> >>
> >>> On Jan 7, 2014, at 4:26 PM, "G. Tim Stone" <[email protected]>
> wrote:
> >>>
> >>> Todd,
> >>>
> >>> I would consider this a Platform and apply 8.15.6, 2010 ed.
> >>>
> >>> Regards,
> >>> G. Tim Stone
> >>>
> >>> G. Tim Stone Consulting, LLC
> >>> NICET Level III Engineering Technician
> >>> Fire Protection Sprinkler Design
> >>> and Consulting Services
> >>>
> >>>             117 Old Stage Rd. - Essex Jct., VT. 05452
> >>> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
> >>>                        [email protected]
> >>>
> >>>
> >>>> -----Original Message-----
> >>>> From: [email protected]
> >>>> [mailto:[email protected]] On Behalf Of
> >>> Steven
> >>>> Scandaliato
> >>>> Sent: Tuesday, January 07, 2014 4:20 PM
> >>>> To: [email protected]
> >>>> Subject: RE: concealed space definition
> >>>>
> >>>> Today...it is whatever you and the AHJ agree on.  Hopefully (fingers
> >>>> crossed) we will have a clear definition in the next edition as we are
> >>>> working at adding the "gaps and clouds" section and with this will
> come
> >>> new
> >>>> definitions including concealed spaces and the 4ft rule.  Hold your
> >>> breath!
> >>>> Haha.
> >>>>
> >>>> Steven Scandaliato, SET CFPS
> >>>> 520.971.2322 Cell
> >>>> Skype: steven.scandaliato
> >>>>
> >>>>
> >>>> -----Original Message-----
> >>>> From: [email protected]
> >>>> [mailto:[email protected]] On Behalf Of
> > Todd
> >>> -
> >>>> Work
> >>>> Sent: Tuesday, January 07, 2014 3:12 PM
> >>>> To: [email protected]
> >>>> Subject: concealed space definition
> >>>>
> >>>> Is there an official definition of a concealed space? Is a 10 ft x 20
> ft
> >>>> platform that is 9" off the ground but not enclosed on the sides
> >>> considered
> >>>> a concealed space?
> >>>>
> >>>> Todd G Williams, PE
> >>>> Fire Protection Design/Consulting
> >>>> Stonington, CT
> >>>> www.fpdc.com
> >>>> 860-535-2080 (ofc)
> >>>> _______________________________________________
> >>>> Sprinklerforum mailing list
> >>>> [email protected]
> >>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
> >>>> firesprinkler.org
> >>>>
> >>>> _______________________________________________
> >>>> Sprinklerforum mailing list
> >>>> [email protected]
> >>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
> >>>> firesprinkler.org
> >>>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)