I think it comes down to if the street elbows are made according to the 
appropriate ASTM standard from Table 6.4.1. In your defense, 6.4.6.1 states 
that unless circumstances exist where hex bushings are allowed, one piece 
reducer fittings shall be used for a change in pipe size.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)