And this focus on 'percent by volume' has got to be the silliest aspect of this 
whole mess, as if we know the exact cubic feet of the inside of all the pipe 
and fittings ;)

> On Jan 28, 2014, at 7:27 PM, Brad Casterline <[email protected]> wrote:
> 
> Hey Jerry this is Brad,
> I hope you don't mind me chiming in again while you wait for experts.
> If you believe your clients will never have 6 big dry Christmas trees fully 
> engulfed in their living room say when the head activates, then it really 
> doesn't matter what psi or k you use.
> 
>> On Jan 28, 2014, at 5:29 PM, [email protected] wrote:
>> 
>> Cecil and Forum:
>> 
>> Sorry to read of your diappointment, Cecil - I feel, however, you are 
>> putting a few words in my mouth. What I was actually saying is: Based on Mr. 
>> Fleming's presentation in Seattle a few years ago, I continue to feel 
>> confident 
>> the systems I design for new homes do NOT pose a risk and/or hazard for 
>> owner/occupants. My memory may be a little "hazy", but I seem to recall Russ 
>> saying his presentation was based on two (or three) separate independent 
>> laboratory tests. I remember his - or my - comparison with the traditional 
>> 'fire 
>> triangle' (remove one component and no combustion/explosion).
>> 
>> I would prefer to put your statement like this: My confidence level is very 
>> high that my Client(s) will not experience an anti-freeze "event" so long 
>> as my designs are based on low pressure levels (Northern NM wells at 40 to 
>> 45 
>> psi), 'k' factors at 4.9+ and glycerin concentrations at NTE/pre-mix 48% 
>> (all combined, not "either/or"). Using (FP) engineering judgement, AHJ 
>> "approval", historical data, New Mexico sprinkler success stories w/glycerin 
>> enets 
>> - I feel confident enough that I designed my own house using this approach. 
>> If my house blows up tommorrow, you will have been correct. But don't hold 
>> your breath.
>> 
>> I am not suicidal, nor am I stupid (my words). If you think I had the 
>> slightest doubt and went ahead with an anti-freeze design for a 
>> billionaire's 
>> 28,000 sq. ft. house - glycerin THROUGHOUT/not just the attic - then I, too, 
>> am 
>> disappointed. When I see factual data that supports the contention that I 
>> should not be designing glycerin systems in any homes, I will stop said 
>> design and drain down the system in my own house. My position remains based 
>> on my 
>> (current) understanding of laboratory test results.
>> 
>> If someone will correct me here: Am I to understand that (roughly) 
>> half-a-dozen 'events' over some 70+ years of anti-freeze installations is 
>> justification for eliminating all anti-freeze systems? Am I totally "out of 
>> the loop" 
>> in New Mexico? Or, do I recall a few of those (more recent) explosions were 
>> actually attributed to extremely high concentrations of glycol/glycerin??
>> 
>> Where are the "experts" that I expected to hear from - other than Cecil??? 
>> The life you save might be mine???
>> 
>> Regards to All-
>> 
>> Jerry
>> [email protected]
>> Santa Fe, New Mexico
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to