Thanks for that explanation. I was trying to connect the dots but that did it...
Rod at Rapid ________________________________________ From: [email protected] [[email protected]] on behalf of Roland Huggins [[email protected]] Sent: Friday, February 14, 2014 9:20 AM To: [email protected] Subject: Re: Spacing with sloped piping the way to think of it (so that it makes sense) is that max area of coverage as determined along the slope is for ACTIVATION and are of coverage for the calculation is DISCHARGE on the floor. Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Feb 14, 2014, at 6:47 AM, James D. Waite <[email protected]> wrote: > Sorry, I read that too quickly (icemageddon is getting to me). Yes the > overall spacing of 133 is a problem, but you're allowed to calculate the > smaller square footage. Area of protection is along the slope, and > calculated area is horizontal. > > Jimmy Waite, CET - Design Manager _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org