John's right. You need a valve with a switch that is meant to be normally
closed. I know Victaulic makes these and I suspect everyone else does also
though I couldn't testify to that in sprinkler court.


On Mon, Feb 17, 2014 at 2:47 PM, John Denhardt <[email protected]
> wrote:

> Not allowed. Must pick up within two turns of normal position.  We did it
> your way for years but new valves are made that comply with the standard.
>
> Thanks,
> John August Denhardt P.E.
>
> > On Feb 17, 2014, at 5:15 PM, "Forest Wilson Fire Sprinkler Contractor" <
> [email protected]> wrote:
> >
> > Just Change it from NO to NC when you connect the contacts
> >
> >
> > Forest Wilson
> > Fire Sprinkler Contractor
> > 937-736-0425
> >
> > Notice:
> > This message is confidential. It may also be privileged or otherwise
> protected by work product immunity or other legal rules. If you have
> received it by mistake, please let us know by e-mail reply and delete it
> from your system; you may not copy this message or disclose its contents to
> anyone. Please send us by fax any message containing deadlines as incoming
> e-mails are not screened for response deadlines. The integrity and security
> of this message cannot be guaranteed on the Internet.
> >
> > -------- Original message --------
> > From: John Denhardt <[email protected]>
> > Date:02/17/2014  4:56 PM  (GMT-05:00)
> > To: [email protected]
> > Subject: RE: Butterfly valve, monitered or not?
> >
> > Wait a second.
> >
> > It looks like the NFPA 20 committee cleaned this section up in 2013 and
> now allows (thanks Chris for the post)
> >
> > (3) Locking valves open
> > (4) Sealing of valves and approved weekly recorded inspection where
> valves are located within fenced enclosures under the control of the owner.
> >
> > That makes more sense.  We were locking them open for years.
> >
> > The point is that these control valves do not affect the system
> operation.  The worse that could happen is the piping or test header valves
> would freeze and break.
> >
> > About three years ago, the industry (NIBCO and Victaulic that I remember
> off the top of my head) have started providing normal closed butterfly
> valves that are correctly supervised to operate within 2 turns from closed.
>  While these valves are available, they cost more than a normal butterfly
> valve.
> >
> > John
> >
> >
> > John August Denhardt, P.E., FSFPE
> > Strickland Fire Protection Incorporated
> > 5113 Berwyn Road
> > College Park, Maryland 20740
> > Office Telephone Number:  301-474-1136
> > Mobile Telephone Number:  301-343-1457
> > FIRE SPRINKLERS SAVE LIVES - Can you live without them?
> >
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> [email protected]] On Behalf Of
> [email protected]
> > Sent: Monday, February 17, 2014 4:44 PM
> > To: [email protected]
> > Subject: RE: Butterfly valve, monitered or not?
> >
> > Agreed. Most normally closed valves cause something else to happen when
> opened (start a pump or dump a deluge system) and that something else is
> usually alarmed..
> >
> > Ron F
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> [email protected]] On Behalf Of John Denhardt
> > Sent: Monday, February 17, 2014 2:21 PM
> > To: [email protected]
> > Subject: RE: Butterfly valve, monitered or not?
> >
> > Agree.  However, this is similar to a fire pump test header control
> valve. The NFPA 20 committee thought it was important enough to supervise
> the fire pump test header valve.  To me, this is a wasteful requirement but
> it is a requirement.  We need this requirement changed.
> >
> > John
> >
> > John August Denhardt, P.E., FSFPE
> > Strickland Fire Protection Incorporated
> > 5113 Berwyn Road
> > College Park, Maryland 20740
> > Office Telephone Number:  301-474-1136
> > Mobile Telephone Number:  301-343-1457
> > FIRE SPRINKLERS SAVE LIVES - Can you live without them?
> >
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> [email protected]] On Behalf Of Brad
> Casterline
> > Sent: Monday, February 17, 2014 4:07 PM
> > To: [email protected]
> > Subject: RE: Butterfly valve, monitered or not?
> >
> > Douglas,
> >
> > Search the archives for 'full forward flow test control valves'.
> > lots of good stuff and fairly recent.
> > brad
> >
> > -----Original Message-----
> > From: Douglas Hicks [mailto:[email protected]]
> > Sent: Monday, February 17, 2014 2:58 PM
> > To: [email protected]
> > Subject: Butterfly valve, monitered or not?
> >
> > I am going to install a 4" butterfly valve on a sprinkler manifold.
>  This will give us an outlet to perform a Forward Flow.  Does the valve
> need to be monitored or will it be OK to use a chain to lock the valve in
> the closed
> > position?
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to