Then it would be 1000 gpm overall (assuming fully spkrd environment) using the hydraulically most remote 3 standpipes. Sez me.
The preceding is my opinion only. SL -------- Original message -------- From: [email protected] Date:02/26/2014 10:31 AM (GMT-08:00) To: [email protected] Subject: RE: NFPA 14 7.10.1.1.3 (2013) yep -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Wednesday, February 26, 2014 11:31 AM To: [email protected] Subject: RE: NFPA 14 7.10.1.1.3 (2013) Is it all one big ST system with the building risers fed by a common supply in the podium? SL -------- Original message -------- From: [email protected] Date:02/26/2014 9:48 AM (GMT-08:00) To: [email protected] Subject: NFPA 14 7.10.1.1.3 (2013) We have 4 buildngs each less than 80k sqft on a level but they sit on top of a 100k sqft garage. Do we calc 500, 500 in the towers or 500, 250 and pick up another 250 in the garage to get 1000 max? Ron F _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org