Received a shop drawing stating that for the deluge system, the contractor 
would purchase standard fused sprinklers and remove the fusible link.

Now I can't find specific NFPA verbiage that would prohibit this but seems to 
me that a sprinkler that is listed for LH or OH occupancies would not be 
acceptable for an EH deluge system just by popping the link out.  Wouldn't this 
also be modifying the sprinkler post production?

Maybe this is done all the time, but what say ye?


I found this statement in 13,  
"8.4.4 Open Sprinklers.
8.4.4.1 Open sprinklers shall be permitted to be used in deluge
systems to protect special hazards or exposures or in other special locations."

Seems kind of like a DUH, statement.  What other type of sprinkler would you 
use for deluge other than open?


Craig L. Prahl

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to