That's interesting. We have all of ours sealed by our FPE and they
never waiver. I hope the BIA is understanding in this case. It will be
interesting.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
On 3/19/2014 12:13 PM, [email protected] wrote:
Ladies & Gentlemen:
We have run in to similar - not exact - circumstances on BIA Projects both
here in NM and AZ. Long story short - BIA accepted/approved similar
'contradictory' design criteria when an engineering decision/judgement was made
(i.e., plans/calc's 'sealed') by a licensed PE/FPE registered in State of
project. Actually, we have previously gotten around 0.15/OH1 densities when
our drawings were sealed by our FPE.
Regards to All-
Jerry
[email protected]_ (mailto:[email protected])
Jerry D. Watts, SFPE
President & Co-Founder
ACCENT FIRE ENGINEERING INT'L. Ltd*
Santa Fe/Albuquerque/Las Cruces/Silver City/Roswell/Artesia New Mexico
Seattle, WA San Diego, CA Phoenix, AZ San Antonio, TX
(800) 503.1961 nationwide
*Licensed Fire Protection Engineers - Architects/Inspectors/Fire
Investigators: AZ CA CO NM NV NY TX UT KS MD MS
In a message dated 3/19/2014 1:03:59 P.M. Mountain Daylight Time,
[email protected] writes:
We are looking at a project with the BIA (Bureau of Indian Affairs).
They require all bldgs over 2000 sq ft to be Ord Grp I as a minimum in
ALL areas. We have dealt with them in the past and there seems to be no
waivering on this issue. We had a contractor in the past install Tyco
BB heads and calc'd for 0.15 gpm. Tyco had written letters that
calculating to 0.15 would be fine. But the data sheet for those heads
says light hazard. So, the BIA rejected and the attic had to be
re-piped for SSU for protection.
Now, the current project has concealed combustible spaces requiring the
specially listed heads for flat, shallow concealed combustible spaces -
Tyco CC, Viking COIN, etc.. However, we are going to have the problem
that these heads are listed for light hazard only. We can't go to SSU
because NFPA 13 states that you must use specially listed heads for
these concealed spaces. We are awaiting a response from the BIA, but I
am not expecting much help. Have any of you ever run into this? If so,
how did you address it? We can't use the only heads listed for the area
because they are only listed as light hazard and the BIA requires all
areas to be OH1 minimum. We can't use SSU sprinklers because NFPA 13
prohibits their use in these spaces. It is a true Catch 22.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org