We are looking to apply NFPA 13 clause 20.3.7 to an existing building where the 
tenant is a Bulk hardware retailer.  This is an alternative to our own national 
sprinkler standard which does not cater to these types of stores very well.
NFPA does not seem to have a lot of information about this particular clause, 
even in the handbook - the figures show various fire tests with the K36 (K25.2 
imp) sprinkler but they do not seem to show a figure that represents this 
clause with the 6m (20ft) storage under a 9.1m (30ft) roof, so we are looking 
for more information on how this is applied to determine if it is suitable.
Perhaps the fire testing information might be available?  Or examples of 
storage in other stores where this has been applied and approved.

An overview of the storage existing:
We cannot use the other options under 20.3 as Extended Coverage heads are not 
considered suitable for the roof construction.  Roof is 8.1m (26.5 ft) storage 
generally max 6m (20ft)
Storage/Display is in a variety of formats, but is all made from racking 
members with solid shelves.
Transverse flues are a marginal 75mm after considering obstructions from the 
braces.
There are lots of open top containers.  Although very few on the upper levels.
There are single row racks which are built with a gondola or back-to-back type 
arrangement on the lower levels (solid back at centre) and standard single row 
rack storage above. Overall width generally 1.1m (3.5 ft)
There are double row racks with various flue gaps. Overall widths from 1.5 to 
2.5m (4.9 to 8.2 ft).  Longitudinal Flues generally from 150 to 350mm (6 to 
13.5 inches)
There are many instances where flues are partially blocked due to large boxes 
within the shelves pushed back, and also pallets on the top levels that 
overhang more at the back that the front.
There are many display areas with solid backs. Some are within the single row 
gondola racks.  Most are in double row racks - some remove the longitudinal 
flues.  Some would fall under the definition of back-to-back racks being 1.5m 
(4.9ft) wide, others exceed this width.
There are some large overhead lighting displays. 1.233 x 2.72 m = 3.35m² (0.66 
x 1.5 ft = 36.1 ft²)

Any assistance is much appreciated.
Thankyou

Nicky Marshall
Southern Regional Manager
PROTECH DESIGN LIMITED
Specialist Fire Protection Consultants
Phone: 03 579 5577  Mobile: 021 433 488  Email: [email protected]  
Skype: nicky-marshall Web:www.protechdesign.co.nz
Address:105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ Postal:PO Box 4022, 
Redwood Village, Blenheim 7242, New Zealand

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to