Good words and thoughts Ken. I liken this situation to every sprinkler design  
aspect I do; I do the 'leg work' and present it to a P. E., for verification. I 
feel like an X-ray technician in this regard-- I know how to run the machine, 
but I would not feel comfortable making any final diagnosis or plan of action 
with-out giving it to the Doctor first:)

> On Apr 4, 2014, at 8:21 PM, Parsley Consulting <[email protected]> 
> wrote:
> 
> Jerry,
>    I appreciate the difficulty you're facing, and I don't envy that sort of 
> problem.  Before I sought the services of a registered PE to certify the 
> hanger assembly, I'd spend a little time on the phone with the good people at 
> the hanger manufacturer, there are two of them located very close to us and I 
> would imagine they might be able to provide a listed assembly to accomplish 
> the support of the piping in the manner your example noted.
> 
>    Baring that, you have no alternative, Brad's math and guidance aside, but 
> to use the services of a PE.  You can't use non-listed components unless 
> they're endorsed by a PE (9.1.2, 9.1.1.5.1).   I take that back, you can do 
> anything you like, whether it's approved for installation by the AHJ is the 
> determinant, and if something happens, you're still wrong, particularly if 
> what you "design" fails.  And it's relevant, I think to note that while Brad 
> has correctly explained the formula for calculating the required section 
> modulus for a cantilevered beam, the information he provided hasn't addressed 
> the means of fastening it to the structure, and the capacity of that means, 
> which is half the question.
> 
>    You're not an engineer, so why take that sort of liability on yourself?  
> Sure, from what I've seen of your submittals in the past you could do the 
> math just fine, but ask yourself this - can you defend it in court?  If the 
> answer is "no", then a manufacturer is the first stop, and a PE is the next.
> 
>    Hope it works out for you.
> *Ken Wagoner, SET
> *Parsley Consulting***
> *350 West 9th Avenue, Suite 206
> *Escondido, CA 92025-5053
> *****Phone 760.745.6181*
> Visit our website <http://www.parsleyconsulting.com/>
> 
> ***
>> On 4/4/2014 5:31 PM, Brad Casterline wrote:
>> Required Section Modulus for cantilevered will be the force (pounds) times 
>> the distance (inches), divided by the stress (15,000). The force is the 
>> weight of the water-filled pipe plus 250. The distance is 4" in this case. 
>> Not hanging at 15' just means the force will be less, i.e, if you have these 
>> unistrut at 7'-6", the weight will be half that if they were 15'-0, but you 
>> still have to add 250 lbs to get the force. Please post your results so we 
>> can all look at them, and be prepared to be criticized for not hiring a 
>> structural engineer. The 4x thing you mentioned will also be cleared up 
>> because with regular trapeze it is half the force times half the distance.
>> Brad Casterline
>> 
>>> On Apr 4, 2014, at 6:56 PM, "Jerry Van Kolken" <[email protected]> wrote:
>>> 
>>> I have a retrofit project where I structure will not allow us to install
>>> beam clamps. The existing hangers are unistrut clamp to the beams and
>>> extended 4" out to allow rod a ring to be attached.  I would like to use a
>>> similar assembly but I don't know how to calculate the loading to determine
>>> the size of the unistrut. I've heard some stuff about 4x the section modulus
>>> based on the trapezes table in NFPA.
>>> 
>>> 
>>> 
>>> I was also wondering if there is a adjust the section modulus if you are not
>>> planning on hanging at 15'-0"?
>>> 
>>> 
>>> 
>>> 
>>> 
>>> Jerry Van Kolken
>>> 
>>> Millennium Fire Protection Corp.
>>> 
>>> 101 Copperwood Way, Suite H
>>> 
>>> Oceanside, CA 92058
>>> 
>>> (760) 722-2722 FX 722-2730
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to