I would think you could subtract the requirements for light and heat, in an 
emergency, from what the fire pump motor needs. Emerg

> On Apr 5, 2014, at 12:11 PM, "Don Lowry" <[email protected]> wrote:
> 
> References from NFPA-20 (2010 edition) 
> 
> Situation:
> 
> Fire Pump to be installed on ESFR system  (75 hp) electric motor.
> 9.2.2 (1) or (5)
> 
> On down through Chapter 9  to;
> 
> 9.2.3.4 Where the overcurrent protection permitted by 9.2.3
> is installed, the overcurrent protection device shall be rated to
> carry indefinitely the sum of the locked rotor current of the
> fire pump motor(s) and the pressure maintenance pump motor(
> s) and the full-load current of the associated fire pump
> accessory equipment.
> 
> OK, so the locked rotor current is 543 amps, plus jockey pump, lights, heat,
> etc added would require a 600 amp over current protective device.  This is
> what the Engineer and I determined would be the requirement for this
> dedicated service to the fire pump.
> 
> When the engineer submitted his electrical service plan (600 amp service) to
> the city, the City Plan Reviewer states that we don't need a 600 amp
> service, but rather a 125 amp service.
> 
> In reading through Article 695.4 of the NEC. It states:
> "Where the locked rotor current value does not correspond to a standard
> overcurrent device size, the next standard overcurrent device size shall be
> used in accordance with 240.6.  The requirement to carry the locked rotor
> currents indefinitely shall not apply to conductors or devices other than
> overcurrent devices in the fire pump motor circuits." 
> 
> So, does this mean that the service itself (transformer) and related
> conductors can be per normal size (125 amp) with just a 600 amp fuse in the
> disconnect before the controller?
> 
> In 30 + years this is the first time I have ever been asked about this.
> Before I was only asked about pump size etc , and when installed and checked
> at pump start-up there was indeed a fuse of appropriate size in the service
> disconnect.  So I assumed all was correct.  I'm just wanting to make sure
> the Engineer and I understand the requirements for the actual electrical
> service provided.  I know it's not my area of expertise, nor my
> responsibility, just curious.
> 
> Thanks in advance for any help.
> 
> Don Lowry, CET, RME (TX)
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to