There doesn't seem to be an exception in 2010, that's the latest we have in the 
office. Since PA is still working out 2007 the powers that be haven't seen fit 
to order the latest one.


Richard Mote ET
Design Manager
Rowe Sprinkler Systems, Inc.



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Wednesday, April 09, 2014 10:55 AM
To: [email protected]
Subject: Re: Diesel fuel tank

Is there.no exception in 20 if A double wall uL 142 tank.
Ron f

Sent from my iPhone

> On Apr 9, 2014, at 7:27 AM, "Richard Mote" <[email protected]> wrote:
> 
> We had the builder layup 3 or 4 courses of 8" CMU block and had them coat the 
> inside with a fuel proof coating. On one job they basically had the inside 
> fiber glassed.
> We just told the GC what was required in terms of cubic feet of containment, 
> and put back on them to build it.
> 
> 
> Richard Mote ET
> Design Manager
> Rowe Sprinkler Systems, Inc.
> 
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> Martinez, Dewayne
> Sent: Wednesday, April 09, 2014 8:33 AM
> To: [email protected]
> Subject: RE: Diesel fuel tank
> 
> Was the containment nothing more than concrete curbs around the tank?
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> Bobby Gillett
> Sent: Wednesday, April 09, 2014 7:30 AM
> To: [email protected]
> Subject: Re: Diesel fuel tank
> 
> The last couple FM projects I did also required both, and the containment 
> dike had to contain 130% of the capacity of the tank.
> 
> Bobby Gillett
> *Living Water Fire Protection, LLC*
> 1160 McKenzie Rd.
> Cantonment, FL 32533
> (850) 937-1850
> livingwaterfp.com  <http://livingwaterfp.com/>
> 
> 
> On Wed, Apr 9, 2014 at 7:07 AM, Richard Mote
> <[email protected]>wrote:
> 
>> The last couple of FM jobs I've done required both a double wall tank 
>> and a containment dike.
>> 
>> NFPA 20, 2010 11.4.1.2.4 Fuel tansk shall be enclosed with a wall, 
>> curb or dike sufficient to hold the entire capacity of the tank.
>> 
>> This isn't in the 2007 edition at least not in the fuel tank section, 
>> so it must be new.
>> 
>> Richard Mote ET
>> Design Manager
>> Rowe Sprinkler Systems, Inc.
>> 
>> 
>> 
>> 
>> -----Original Message-----
>> From: [email protected] [mailto:
>> [email protected]] On Behalf Of 
>> Martinez,
> 
>> Dewayne
>> Sent: Wednesday, April 09, 2014 7:45 AM
>> To: SprinklerFORUM
>> Subject: Diesel fuel tank
>> 
>> We have an existing system with a diesel fuel pump and tank(280gpm) 
>> that was installed back in 1991.  The insurance carrier is requesting 
>> that either a new duel wall tank or a dike containment system be
> installed.
>> I have looked through NFPA 20 and didn't see anything requiring
> either.
>> Should I be looking in a different place?
>> 
>> Thanks,
>> 
>> Dewayne
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l er.org _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l
>> er.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to