I'd disagree. 13R limits you to using only residential sprinklers throughout except in "dwelling units meeting the definition of a compartment, as defined in Section 3.3, where no more than four sprinklers are located in the dwelling unit," where QR are permitted, whereas 13, which requires QR in light hazard occupancies permits an exception and allows residential heads, "in dwelling units and their adjoining corridors, provided they are installed in conformance with their listing." (based on the 2010 editions of 13 & 13R as cited in BJ Newlin's previous post)
On Fri, Apr 18, 2014 at 5:57 AM, BJ Newlin <[email protected]>wrote: > Sorry I hit the send button toofast > > NFPA 13 2010 ed. > > > 8.4.5 Residential Sprinklers. > > 8.4.5.1* Residential sprinklers shall be permitted in dwelling > units and their adjoining corridors, provided they are installed > in conformance with their listing. > > 8.4.5.2 Residential sprinklers shall be used only in wet systems > unless specifically > > > My interpretation is that you can use residential sprinklers only in > dwelling units and their corrirods in an NFPA 13 building. > > BJ Newlin > Service Sales > Aegis Fire Protection LLC. > > "Whoever is careless with the truth in small matters cannot be trusted with > important matters" > ― Albert Einstein > > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of > Martinez, Dewayne > Sent: Friday, April 18, 2014 7:53 AM > To: [email protected] > Subject: Residential dwelling unit sprinklers > > NFPA 13 and 13R (07ed) > > Please refresh my memory since it has been awhile since I did residential > work. If the building is classified as 13R I must use residential > sprinklers in the dwelling unit OR I can use QR sprinklers if the dwelling > unit is 4 heads or less(6.7.7.1.3). For a NFPA 13 building I can use > either > as long as I design and calculate them per their listings....sound correct? > > Thanks, > > Dewayne > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) A problem well stated is a problem half solved. -Charles F. Kettering, inventor and engineer (1876-1958) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org