The code section provides two means, the first is prescriptive the second 
performance. A performance based design would require the services of a 
professional engineer who would submit a signed and sealed design package 
demonstrating methods and materials, calculations to meet the performance 
requirement, or a tested and listed system by a nationally recognized testing 
laboratory meeting the performance requirement of the code.  In summary some 
choose prescriptive methods as a way to avoid the design aspects. On site 
destructive testing is not stipulated.     
John Drucker

-----Original Message-----
From: Owen Evans <[email protected]>
Sender: <[email protected]>
Date: Fri, 18 Apr 2014 10:54:19 
To: <[email protected]>
Reply-To: <[email protected]>
Subject: Bollards, 312.3 Other barriers

                                                
                        
                                
                                        
If a contractor decides to go with 312.3 Other barriers, must that contractor 
provide a witnessed test of the barriers or provide some type of documentation 
that states the barriers will stand-up to 12,000 pounds applied at 36 inches?


Owen Evans


IFC 312.1 General. Vehicle impact protection required by this code shall be 
provided by posts thatcomply with Section 312.2 or by other approved physical 
barriers that comply with Section 312.3.
                                        
312.2 Posts. Guard posts shall comply with all of the following requirements:
                                        
                                                
                                                        
Constructed of steel not less than 4 inches in diameter and concrete filled.
                                                
                                                
                                                        
Spaced not more than 4 feet between posts on center.
                                                
                                                
                                                        
Set not less than 3 feet deep in a concrete footing of not less than a 15 inch 
diameter.
                                                
                                                
                                                        
Set with the top of the posts not less than 3 feet above ground.
                                                
                                                
                                                        
Located not less than 3 feet from the protected object.
                                                
                                        
                                        
312.3 Other barriers. Physical barriers shall be a minimum of 36 inches in 
height and shall resist a forceof 12,000 pounds applied 36 inches above the 
adjacent ground surface. 
                                
                        
                
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to