The code section provides two means, the first is prescriptive the second performance. A performance based design would require the services of a professional engineer who would submit a signed and sealed design package demonstrating methods and materials, calculations to meet the performance requirement, or a tested and listed system by a nationally recognized testing laboratory meeting the performance requirement of the code. In summary some choose prescriptive methods as a way to avoid the design aspects. On site destructive testing is not stipulated. John Drucker
-----Original Message----- From: Owen Evans <[email protected]> Sender: <[email protected]> Date: Fri, 18 Apr 2014 10:54:19 To: <[email protected]> Reply-To: <[email protected]> Subject: Bollards, 312.3 Other barriers If a contractor decides to go with 312.3 Other barriers, must that contractor provide a witnessed test of the barriers or provide some type of documentation that states the barriers will stand-up to 12,000 pounds applied at 36 inches? Owen Evans IFC 312.1 General. Vehicle impact protection required by this code shall be provided by posts thatcomply with Section 312.2 or by other approved physical barriers that comply with Section 312.3. 312.2 Posts. Guard posts shall comply with all of the following requirements: Constructed of steel not less than 4 inches in diameter and concrete filled. Spaced not more than 4 feet between posts on center. Set not less than 3 feet deep in a concrete footing of not less than a 15 inch diameter. Set with the top of the posts not less than 3 feet above ground. Located not less than 3 feet from the protected object. 312.3 Other barriers. Physical barriers shall be a minimum of 36 inches in height and shall resist a forceof 12,000 pounds applied 36 inches above the adjacent ground surface. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org