Sounds like a 13R to me.

I'm not so sure about the assessment of 7.3.1 criteria for the garage - I
wouldn't think a two hour separation is enough to classify the garages as a
'separate building'. That's usually when you have residential over a
parking garage structure - think podium style. I would be looking more into
7.3.2.

It sounds like you're on the right track - I would double check your local
ammendments, the architect's code analysis and any specs or insurance
requirements that may require more than 13r.




On Mon, Apr 21, 2014 at 10:17 PM, George Medina Jr <[email protected]> wrote:

>
>
> Forum,
> Can anyone please add there 2 cents in and help clarify when to classify
> as a 13 system versus a 13R
> I have a project that consist of 3 stories with an occupancy of R2/S2 and
> Construction Type VA. The project is lay ed out like a horse shoe
> with 3 sides  and a corridor running down the middle from  1 required
> stairwell to another on the opposite end, with a court yard in the middle.
> There are private garages around the perimeter of the building (which all
> have access from a common 1st floor corridor only) All the Garages have a 2
> hour separation between them and the 2nd level  residential units and the
> 1st floor corridor. There are residential units on the 1st floor (opposite
> the garages) facing the court yard.
>
> I figured the Garage calculations shall conform to NFPA-13, based on
> NFPA-13R (2013ed.) Sec. 7.3.1. My question is if the building can be
> classified as a 13R (with garage areas calced at NFPA-13) or should it be
> classified as a NFPA-13 with dwelling units & residential heads
> (calculations based on the greater of the area/density @ .10 or the head
> listing). If not, what is the determining factor or the threshold.
>
>
>
>
>
> George Medina Jr.
> Mobile: 323-906-5701
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



On Mon, Apr 21, 2014 at 10:17 PM, George Medina Jr <[email protected]> wrote:

>
>
> Forum,
> Can anyone please add there 2 cents in and help clarify when to classify
> as a 13 system versus a 13R
> I have a project that consist of 3 stories with an occupancy of R2/S2 and
> Construction Type VA. The project is lay ed out like a horse shoe
> with 3 sides  and a corridor running down the middle from  1 required
> stairwell to another on the opposite end, with a court yard in the middle.
> There are private garages around the perimeter of the building (which all
> have access from a common 1st floor corridor only) All the Garages have a 2
> hour separation between them and the 2nd level  residential units and the
> 1st floor corridor. There are residential units on the 1st floor (opposite
> the garages) facing the court yard.
>
> I figured the Garage calculations shall conform to NFPA-13, based on
> NFPA-13R (2013ed.) Sec. 7.3.1. My question is if the building can be
> classified as a 13R (with garage areas calced at NFPA-13) or should it be
> classified as a NFPA-13 with dwelling units & residential heads
> (calculations based on the greater of the area/density @ .10 or the head
> listing). If not, what is the determining factor or the threshold.
>
>
>
>
>
> George Medina Jr.
> Mobile: 323-906-5701
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to