That is absolutely not accurate and there is nothing in any code or
standard that ties the basis of sprinkler system design to whether or
not a building has standpipes.  A careful read of the applicable
sections of 14 will reveal that the prescriptives for valving and
connection of sprinklers to standpipes are all generic and do not
distinguish between a "13" and a "13R".

Your AHJ may want to retrieve the code books he or she has previously
thrown away, thinking in error that they already know everything.   I
would make diplomatic request of this person to cite the applicable
language that supposedly backs this up.

My opinion only,
SML



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Travis Mack
Sent: Monday, April 28, 2014 11:16 AM
To: [email protected]
Subject: Combination standpipe system = NFPA 13???

I have a project that qualifies for NFPA 13R per architectural code
study.  The project construction type, square foot, etc allows us to
follow NFPA 13R per IBC.

This is a 4 story building and has manual wet standpipes due to building
height.  The AHJ is stating that because we have a combination
standpipe, it is required to be an NFPA 13 system.  Has anyone ever run
into this?  I have never heard of this requirement. If it is true, an
easy fix would be to run a separate sprinkler system riser.  I have just
never heard of this and have done hundreds of projects at 13R with
combination standpipes.

The same reviewer is stating that since it is required to be an NFPA 13
system because of the standpipes, we also have to use a minimum 5.6k
sprinkler.  I KNOW this is wrong, so I truly question the issue above.  
Any thoughts on this?

--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to