Beam rule: Check

3X rule which only applies to structural members in LH: Check

Last would be Suspended or Flr mounted obstructions of 8.6.5.2.2 but it
states "The distance from sprinklers to privacy curtains, freestanding
partitions, room dividers, and SIMILAR obstructions". I like the suspended
part but not the "& similar obstructions" part as all the examples shown
and discussed are varying types of partitions which obstruct sprinkler
discharge from reaching the other side. I don't think a suspended duct is
similar in that regard. Nevertheless - it looks like 8.6.5.2.2 is it?


On Mon, May 19, 2014 at 3:44 PM, Roland Huggins
<[email protected]>wrote:

> The continuous obstruction requirement to apply the beam rule kicks in
> only when the top of the obstructions is level with or above the plane of
> the sprinkler deflector (section 8.6.5.2.1.2).  If extended coverage then
> even if the top of the obstruction is below the plane of the deflector, the
> beam rule applies.
>
> Roland
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
>
>
> On May 19, 2014, at 2:32 PM, IPA <[email protected]> wrote:
>
> Too much tunnel vision right now:
>
> Which obstruction criteria would one use for ductwork 16" below the roof
> deck with 6" clear space between the duct and the roof and the sprinkler
> deflector at 4" below deck in a light hazard office?
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>