Beam rule: Check 3X rule which only applies to structural members in LH: Check
Last would be Suspended or Flr mounted obstructions of 8.6.5.2.2 but it states "The distance from sprinklers to privacy curtains, freestanding partitions, room dividers, and SIMILAR obstructions". I like the suspended part but not the "& similar obstructions" part as all the examples shown and discussed are varying types of partitions which obstruct sprinkler discharge from reaching the other side. I don't think a suspended duct is similar in that regard. Nevertheless - it looks like 8.6.5.2.2 is it? On Mon, May 19, 2014 at 3:44 PM, Roland Huggins <[email protected]>wrote: > The continuous obstruction requirement to apply the beam rule kicks in > only when the top of the obstructions is level with or above the plane of > the sprinkler deflector (section 8.6.5.2.1.2). If extended coverage then > even if the top of the obstruction is below the plane of the deflector, the > beam rule applies. > > Roland > > Roland Huggins, PE - VP Engineering > American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives > Dallas, TX > http://www.firesprinkler.org > > > On May 19, 2014, at 2:32 PM, IPA <[email protected]> wrote: > > Too much tunnel vision right now: > > Which obstruction criteria would one use for ductwork 16" below the roof > deck with 6" clear space between the duct and the roof and the sprinkler > deflector at 4" below deck in a light hazard office? > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org