Is a main relief valve allowed in this case - see NFPA 20.  Most likely not!

John

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Tuesday, May 20, 2014 12:13 PM
To: Martinez, Dewayne; [email protected]
Subject: RE: Pressure reducing valve on fire pump

Dewayne:

Why a reducing valve instead of a relief valve?    If the excess
pressure is at churn only, then a relief valve would be the ticket as it only 
occurs in a no-flow condition.  This would mitigate Pete's concerns about 
redundancy as prescribed in NFPA 14.

SML

 




-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Martinez, 
Dewayne
Sent: Tuesday, May 20, 2014 5:20 AM
To: [email protected]
Subject: Pressure reducing valve on fire pump

We have a situation where we have a pump that produces more than 175psi at 
churn.  Can we put in a main pressure reducing valve after the pump discharge 
to bring it all down to 175psi or do we need one for each system?

Thanks,

Dewayne  

 