Then I will count on your support for the next cycle.....

________________________________________
From: Sprinklerforum [[email protected]] on behalf 
of Steve Leyton [[email protected]]
Sent: Friday, May 23, 2014 2:02 PM
To: [email protected]
Subject: RE: Sprinkler Systems

Agreed about losing Class II.   And that I'm correct.






-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Pete Schwab
Sent: Friday, May 23, 2014 11:05 AM
To: [email protected]
Subject: RE: Sprinkler Systems

Agreed that you are correct or that you would support losing/removing
Class II standpipes from NFPA 14???


________________________________________
From: Sprinklerforum [[email protected]] on
behalf of Steve Leyton [[email protected]]
Sent: Friday, May 23, 2014 1:58 PM
To: [email protected]
Subject: RE: Sprinkler Systems

Agreed.   ;-)






-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Pete Schwab
Sent: Friday, May 23, 2014 10:57 AM
To: [email protected]
Subject: RE: Sprinkler Systems

Steve is correct... My utmost and sincere apologies... I meant to say
"trained fire Brigade".... We need to lose Class II standpipes


________________________________________
From: Sprinklerforum [[email protected]] on
behalf of Steve Leyton [[email protected]]
Sent: Friday, May 23, 2014 1:48 PM
To: [email protected]
Subject: RE: Sprinkler Systems

I don't wanna nit-pick too much, but the current definitions and classes
of standpipe systems makes NO provision for occupant use.   I agree with
Pete that the likely use of the term Shotgun is reference to a riser
that doesn't have a control valve and may also not have a check valve.
Out here in fair weather country we put our backflows out at the
property line with FDC's attached to the discharge side, comprising a
complete control-check-FDC manifold.   It is very common to see a
"riser" comprised of no more than a gauge, flow switch and test/drain
valve.

SML






-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Smith, David L.(FAC)
Sent: Friday, May 23, 2014 10:45 AM
To: [email protected]
Subject: RE: Sprinkler Systems

Thanks for clarifying that for me Pete

David L. Smith
Fire Protection Maintenance
City of Lakeland
Public Works / Facilities
228 S. Massachusetts Ave.
Lakeland, Fl. 33801
Office: 863-834-2380
Fax:  863-834-2284
Cell: 863-559-0903
[email protected]



-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Pete Schwab
Sent: Friday, May 23, 2014 1:45 PM
To: [email protected];
[email protected]
Subject: RE: Sprinkler Systems

David
I am not familiar with a shotgun system. A standpipe system will be a
system that has hose valves for occupant or fire department use. These
days we usually only see standpipes for fire department use. A standpipe
system can also have connections to sprinkler systems. (Typical for 4
story or taller buildings in Florida).
I have heard of a "Shotgun" riser. This is almost always a riser for a
sprinkler system that has a control valve and a check valve. The check
valve has a drain attached to it as well as the gauge assemblies.
I have pasted a link (not sure if it will come through on this forum) to
a "shotgun" riser check valve.

https://imail2.waynefire.com/owa/?ae=PreFormAction&a=ReplyAll&t=IPM.Note
&id=RgAAAADUIy2uEn7QEb6WAKDJDFRrBwBp%2fZ7LzzilS4i%2fDgCOx7xRAAAlYgAoAAAK
Lb28HRUFToXdF0nAlaEnAAAAFMC8AAAJ&pspid=_1400861904231_553169776

Pete

________________________________________
From: Sprinklerforum [[email protected]] on
behalf of Smith, David L.(FAC) [[email protected]]
Sent: Friday, May 23, 2014 1:31 PM
To: [email protected]
Subject: Sprinkler Systems

Can someone explain to me the definition of a Standpipe system and a
shotgun system?

David L. Smith Member
Fire Protection Maintenance
City of Lakeland
Public Works / Facilities
228 S. Massachusetts Ave.
Lakeland, Fl. 33801
Office: 863-834-2380
Fax:  863-834-2284
Cell: 863-559-0903
[email protected]<mailto:[email protected]>



________________________________

PUBLIC RECORDS NOTICE:

All e-mail sent to and received from the City of Lakeland, Florida,
including e-mail addresses and content, are subject to the provisions of
the Florida Public Records Law, Florida Statute Chapter 119, and may be
subject to disclosure.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________