I'd tell the engineer to site the code section that prohibits the pipe passing 
through. It's ridiculous but I have seen AHJ's interpret the thing about "no 
unnecessary equipment" to mean the pipe can enter but not leave an electrical 
equipment room. I don't think there is any code at all about pipe in a telecom 
room.
Ron F

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jerry Van Kolken
Sent: Thursday, May 29, 2014 8:29 AM
To: [email protected]
Subject: RE: telecom rooms

I only have a copy of 08' NEC 110.26, but according to that any elec. Panels 
you need to be 6'-0" above, or clear the equipment, unless there is a ceiling 
in the room. I don't know if that applies to telecom panels. The only time I've 
been told I can't run through a telecom room is military projects so it might 
be a UFC requirement.

Jerry Van Kolken
Millennium Fire Protection
(760) 722-2722

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Travis Mack
Sent: Thursday, May 29, 2014 8:18 AM
To: [email protected]
Subject: telecom rooms

Is there anything in any code/standard that prohibits sprinkler piping from 
passing through telecom rooms?  I don't have access to the NEC right now.  I 
can't locate anything in NFPA 13 that would prohibit it.

I am on a project where due to phasing, I have to run a branch line through the 
telecom room to supply 2 sprinklers on the other side of it for this phase.  
The engineer says you can't do it. I thought I remember something in the NEC 
saying that sprinkler piping was acceptable to pass through these electric and 
telecom rooms.  I just can't run over panels.

--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to