There is a header in the riser room with one riser for the basement sprinkler 
system (w/ control valve) and another riser for the standpipes (no control 
valve).  One of the standpipe stairwell risers will be a combined standpipe / 
sprinkler with the correct control/check valves installed per NFPA. 
I guess I could bring the basement system off the standpipe riser if needed.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Friday, June 06, 2014 9:27 AM
To: [email protected]
Subject: RE: control valve on standpipe bulk main?

How are the sprinkler mains configured after the stand pipe bulk main branches 
off?


SteveĀ 

<div>-------- Original message --------</div><div>From: "Martinez, Dewayne" 
<[email protected]> </div><div>Date:06/06/2014  6:43 AM  
(GMT-08:00) </div><div>To: [email protected] 
</div><div>Subject: control valve on standpipe bulk main? </div><div> 
</div>NFPA 13 or 14 (07ed)

Situation:

Water supply with BFP supplying one wet system and one standpipe system.
Wet system has a control valve in the riser room but we would like not to put a 
control valve on the standpipe riser / bulk main in order to connect the FDC to 
it father down in the building.  Each stairwell standpipe will have  a control 
valve to isolate it off the standpipe bulk main.  AHJ is requiring an 
additional control valve on the bulk main in the riser room which would require 
us to now run an additional 250ft of 4in pipe to the FDC location.  Of course 
he won't state where he gets this requirement just that he wants it.  I have 
piped several buildings this way in the past.  Have I been doing it wrong all 
these years?

Thanks,

Dewayne





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to