Hello Todd, How are you going to get a pit waterflow signal? Depending on the elevator code it will be required and is not allowed to trip for anything other than the pit head flowing water. I have not found a waterflow switch to use for this. That said in the same situation we have fed the pit head from the wet system on the first floor Control valve and flow switch are on the first floor also, Route the pipe down the shaft to the head location. What you are describing is not allowed by any of the elevator inspectors around here I have had dealings with.
Friday, June 6, 2014, 3:55:08 PM, you wrote: > I am working on a project with 3 levels of offices and a ground > floor parking garage (open therefore dry). The elevator pit is just > below the ground floor and we have to install a sprinkler there. > The contractor asked me how you are supposed to drain the drop in > the pit after a trip test. Any thoughts? > Todd G Williams, PE > Fire Protection Design/Consulting > Stonington, CT > www.fpdc.com > 860-535-2080 (ofc) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org -- Best regards, Charles Thurston mailto:[email protected] Systems Design Manager NICET Certified _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org