..and it's also a bigger problem if you're not dealing with 8" DIP, but 50 yr 
old cast iron pipe. I have seen that differentiation blown off many times, but 
the repercussions CAN be significant. What is the C factor on 50 yr. old cast 
iron? If you can't determine it empirically, then FM may tell you 75 to as low 
as 40. Which equates to about 3.5 psi to 11 psi, respectively, at 400 gpm (& 
1,000 ft.). So which coefficient would you use if FM was not on the job? What 
would "code" require?

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Scott A Futrell
Sent: Thursday, June 19, 2014 9:21 AM
To: [email protected]
Subject: RE: Location of Flow Test in Calc's

Totally agree, however if the concept isn't understood it morphs to the email 
that started this thread.  400 gpm through old 4" or 6" is a bigger problem.

The right way is to calculate to the flow, get the information to do it right.  
If it is a single-feed loop and you are on the remote end of that loop from the 
supply and the test, you need to account for the loss.

Scott

(763) 425-1001x12 Office
(612) 759-5556 Cell

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of IPA
Sent: Thursday, June 19, 2014 9:08 AM
To: [email protected]
Subject: Re: Location of Flow Test in Calc's

In light & ordinary hazards it's usually not a big deal as long as you've 
accounted for elevation differences. 400 gpm flowing through a thousand feet of 
8" DIP equates to a little over 1 psi friction loss.

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to