Thanks - that is what I was looking for. However, now that I see the
wording I know this reviewer will dispute the chain link being a
'structural member' - righly so, more than likely. I think I will just
re-space accordingly and avoid the headache.



On Tue, Jul 8, 2014 at 10:16 AM, Todd - Work <[email protected]> wrote:

> If you go into the definitions section, under Unobstructed Construction,
> it references structural members with openings "at least 70% of the cross
> section area" as being considered unobstructed. This same magical 70% also
> shows up in requirements for mesh in privacy curtains. I think this could
> be extrapolated to include chain link, provided there is over 70% openings
> in the cross sectional area.
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 860-535-2080 (ofc)
>
> > On Jul 8, 2014, at 12:27 PM, "Steve Leyton" <[email protected]>
> wrote:
> >
> > Got it, we see this in condo communities all the time.  Mini-storage,
> > personal tenant storage ... it's all pretty much the same
> > compartmentalization mentality.  IMHO the chain link elements are not
> > obstructions.
> >
> > SL
> >
> >
> >
> >
> >
> >
> > -----Original Message-----
> > From: Sprinklerforum
> > [mailto:[email protected]] On Behalf Of IPA
> > Sent: Tuesday, July 08, 2014 9:24 AM
> > To: [email protected]
> > Subject: Re: Chain Link Partitions in Ord Group II
> >
> > This is a large storage area adjacent to a locker room. The storage room
> > is divided up into little compartments with chain link 'security mesh'
> > while the locker rooms have certain areas that are solid framed up to 2
> > ft from the ceiling which is chain link from there on up. I had it
> > originally layed out as if they were not obstructions but now that I'm
> > starting to finalize everything I'm starting to second guess myself and
> > would like to have backup in case plan review questions it.
> >
> >
> >
> > On Tue, Jul 8, 2014 at 9:19 AM, Steve Leyton
> > <[email protected]>
> > wrote:
> >
> >> I'd take a common sense approach to this.  If sprinklers were jammed
> >> up against this type of divider, they could be obstructed.  But if
> >> storage height and clearance-to-deflector limits are observed, these
> > don't
> >> present an obstruction.  Are you looking at a mini-storage?   Over the
> >> years, have done many of these throughout the Southwest and the use of
> >
> >> chain link - either full height or just the top 2 feet of framed
> >> partitions - has been the go-to means of allowing us to stretch out
> >> sprinkler spacing and not end up with mean coverage of 50-75 sq. ft.
> >> per sprinkler.
> >>
> >> Steve Leyton
> >>
> >>
> >>
> >>
> >>
> >>
> >> -----Original Message-----
> >> From: Sprinklerforum
> >> [mailto:[email protected]] On Behalf Of
> >> IPA
> >> Sent: Tuesday, July 08, 2014 9:16 AM
> >> To: [email protected]
> >> Subject: Chain Link Partitions in Ord Group II
> >>
> >> Would chain link 'partitions' (full height to ceiling) be considered
> >> an obstruction for a storage area in an ordinary group 2 occupancy?
> >> I'm having a hard time coming up with anything for this and the
> >> closest I can think of is the privacy curtain requirement for light
> > hazard.
> >>
> >> Thanks,
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> >> er
> >> .org
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> >> er.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> > .org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org