There is a local AHJ that has recently started comparing the residual
pressure when the Inspector's Test Valve is opened to the Residual Pressure
Demand on the Calc Plate. If the pressure drops below system demand
pressure, they will not sign off on the final occupancy.

The main problem stems from the fact that these jobs are 13R projects and
the inspector's test is at the riser. They are not measuring the flow so
there is no way to know exactly how much friction loss is occurring through
the test connection. I would assume it is substantially higher than what
would occur through the system as designed, but they insist it is the right
way to verify the calcs were done properly.

Has anyone come across this, or have any ideas how to explain to the
building officials?