Travis check out 8.15.1.5 (2). Localized protection looks to be a viable
option. It doesn't matter that you have a continuous 200 ft. corridor.. the
protection only has to be 'localized' in the vicinity of the combustibles.


On Thu, Jul 17, 2014 at 9:34 AM, Travis Mack <[email protected]> wrote:

> The project meets the criteria for not having 3000 sq ft, so we are good
> there.
>
> I question the "localized" idea because I have a corridor that is 200'x8'.
>  There is 60' of space that has these wood framing members.  The space
> above the ceiling is continuous for the 200'. So, just putting sprinklers
> in that 60' doesn't seem to meet the intent of NFPA 13 as I understand it.
>  However, I would be happy to be wrong.  My gut is that we have to protect
> all 200'.  There are 2 of these corridors on each floor.  Because they are
> flat and <36", I believe we need specially listed sprinklers (CC2 or
> equal).  So, we are looking at 17 sprinklers per corridor x 2 corridors x 5
> floors which is an additional 170 sprinklers the installer was not
> anticipating.  I can understand his concern.
>
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> On 7/17/2014 9:26 AM, Bob wrote:
>
>> Not sure what your question " does localized meet anything in NFPA 13" is
>> referring.  Localized certainly meets the criteria of NFPA 13 if the area
>> is
>> an otherwise noncombustible space.  The structure would be "fully
>> sprinklered" per 13, but another point that I just thought of is since
>> this
>> is TJI construction are the channels filled with noncombustible
>> insulation?
>> If not isn't a 3000 sf area required per 11.2.3.1.4?
>>
>>
>> Thank You,
>>
>> Bob Knight, CET III
>> 208-318-3057
>> www.Firebyknight.com
>>
>>
>>
>> -----Original Message-----
>> From: Sprinklerforum [mailto:[email protected].
>> org]
>> On Behalf Of Travis Mack
>> Sent: Thursday, July 17, 2014 10:02 AM
>> To: [email protected]
>> Subject: Re: 8.15.1.2.1 and A8.15.1.2.1 NFPA 13 (2013)
>>
>> Well, does localized meet anything in NFPA 13?  I don't think so.  That is
>> my concern for doing just limited area protection.  Also, since the
>> architect is using the sprinkler system to get the area increase, I don't
>> think that a limited protection of these areas would allow the area
>> increases for a NFPA 13 system.  While it makes sense, I just don't want
>> to
>> be in the grey areas.  These are basically open on 2 ends, so the
>> exception
>> for extending into the unprotected side doesn't apply. If this were only
>> open on one side, that would work.  My gut is telling me that we have to
>> protect the entire 200' corridor.
>>
>> As an additional question to this, even if the AHJ would permit them to be
>> omitted, would that alleviate the designer/installer of liability.
>> My fear is that it will not alleviate the liability. I am pushing to have
>> the space protected or having some other method to make it
>> non-combustible,
>> such as metal hat channels to support the sheet rock.
>>
>> Travis Mack, SET
>> MFP Design, LLC
>> 2508 E Lodgepole Drive
>> Gilbert, AZ 85298
>> 480-505-9271
>> fax: 866-430-6107
>> email:[email protected]
>>
>> On 7/17/2014 8:44 AM, Bob wrote:
>>
>>> T,
>>> This is a very subjective quantity that is up to you and the AHJ to
>>> agree upon.  There are several AHJ'S that I deal with that would agree
>>> that your situation would allow for omission, but I have one AHJ who
>>> would
>>>
>> not agree.
>>
>>> Have you, or are you, considering providing localized protection just
>>> for these areas per NFPA 13 8.15.1.5?
>>>
>>> Thank You,
>>>
>>> Bob Knight, CET III
>>> 208-318-3057
>>> www.Firebyknight.com
>>>
>>>
>>> -----Original Message-----
>>> From: Sprinklerforum
>>> [mailto:[email protected]]
>>> On Behalf Of Travis Mack
>>> Sent: Wednesday, July 16, 2014 2:16 PM
>>> To: [email protected]
>>> Subject: 8.15.1.2.1 and A8.15.1.2.1 NFPA 13 (2013)
>>>
>>> Has anyone been able to determine what is an acceptable amount of
>>> non-structural wood?  We have a hotel project.  It is TJI construction
>>> with sheet rock to the bottom of the TJI throughout the building
>>>
>> construction.
>>
>>> Under that, in the corridor, they have a dropped ceiling that is
>>> acoustical tile and then every +/-40', there is a 15' span of gyp
>>> board ceiling.  The builder is framing the gyp board ceiling with wood
>>> structural members.  In a 200' corridor, there is about 60' of these
>>> gyp board areas.  Would this qualify as an area needing sprinklers or
>>> would you not put sprinklers in this area?
>>>
>>> --
>>> Travis Mack, SET
>>> MFP Design, LLC
>>> 2508 E Lodgepole Drive
>>> Gilbert, AZ 85298
>>> 480-505-9271
>>> fax: 866-430-6107
>>> email:[email protected]
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.org
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.org
>>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
>> org
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
>> org
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to