http://www.nfpa.org/Assets/files/AboutTheCodes/13/Errata13-13-1.pdf

Thanks Ken.

firstin, a co-worker just mailed me the above link, correcting this issue.

Brad  

-----Original Message-----
From: Parsley Consulting [mailto:[email protected]] 
Sent: Tuesday, July 22, 2014 4:11 PM
To: [email protected]
Subject: Re: Bracing

It's a section reference which was not updated from the 2010.  In the 
2010 the requirements for lateral bracing were found in 9.3.5.3.

The section I quoted, 9.3.5.5.10 should reference 9.3.5.5 in the 2013, 
and it was not updated in the code cycle.

It should be noted that the above is my opinion as a member of the NFPA 
Automatic Sprinkler System Hanging and Bracing accordance with the NFPA 
Regulations Governing Committee Projects and should therefore not be 
considered, nor relied upon, as the official position of the NFPA or its 
Committees

*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, CA 92025-5053
*****Phone 760.745.6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 7/22/2014 12:26 PM, Brad Casterline wrote:
> Ken,
>
> Is the section you reference 13-2013? If so should it say 9.3.5.5 shall
not
> apply, not 9.3.5.3?
>
> -----Original Message-----
> From: Parsley Consulting [mailto:[email protected]]
> Sent: Tuesday, July 22, 2014 2:04 PM
> To: [email protected]
> Subject: Re: Bracing
>
> This is unfortunately an all too common mistake.
>
> Section 9.3.5.5.10 allow the omission of lateral sway bracing on mains
> supported by hanger rods whose length is less than 6", measured from the
> top of the pipe to the point of attachment to the structure.  This has
> been a part of NFPA 13 for quite some time.
>
> There is no such allowance for omission of longitudinal bracing in NFPA
13.
>
> Unfortunately I believe the AHJ is in error.
>
> This represents my personal opinion as a member of the hanging and
> bracing committee of NFPA 13, and does not imply the official position
> of the NFPA, which is contained in the body of the document.
>
> *Ken Wagoner, SET
> *Parsley Consulting***
> *350 West 9th Avenue, Suite 206
> *Escondido, CA 92025-5053
> *****Phone 760.745.6181*
> Visit our website <http://www.parsleyconsulting.com/> ***
> On 7/22/2014 11:52 AM, [email protected] wrote:
>> I'm a 13D guy but I have a 13 question. What bracing is required if the
> hangers are 6" or less in lenght? An AHJ said bracing would only be
required
> at the riser. No lateral or longitude required. Is that true? I'm looking
in
> chapter 9 but don't see it.
>
>> Sent from my iPhone
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to