Agree 100% - We do this on many projects.

John

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Wednesday, July 30, 2014 12:35 PM
To: [email protected]
Subject: RE: jockey pump suction

Agreed.  

Nothing stating JP can't be sourced separately from FP.  As long as the 
installation meets NFPA 20 and the FP can sense the drop in system pressure 
when the JP can't handle the flow requirement, you should be fine.


Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Wednesday, July 30, 2014 12:31 PM
To: [email protected]
Subject: RE: jockey pump suction

There's nothing in the 20 that says you can't take suction from a different 
water supply for the jockey pump than the one that serves the fire pump.  I'd 
say that the domestic supply should be reviewed by the AHJ to assure that it 
meets the sniff test for reliability, though
that's not defined.   Any way you look at it, the J-pump is required to
be "approved".

Steve Leyton
Protection Design & Consulting
Anticipating Simon Shannon's Out of Office Reply

 




-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Todd - Work
Sent: Wednesday, July 30, 2014 9:25 AM
To: [email protected]
Subject: jockey pump suction

A client in a rural area has a diesel VT fire pump taking suction from an 
underground 30000 gallon cistern. Their domestic supply is fed from a separate 
well. The jockey pump takes suction from the domestic water supply. Is there a 
problem with this? There is a backflow preventer on the jockey pump suction 
line. 

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to