Thanks Craig, I did end up finding it. This is a non-combustible attic with
limited access, and due to the construction, it wouldn't be possible to use
the space for storage.


On Wed, Aug 20, 2014 at 8:57 AM, <[email protected]> wrote:

> There are provisions for omission of sprinklers in specific areas.
> Electrical rooms are one example I run into quite often.  BUT, in order to
> omit the sprinklers, other construction and operational measures must be
> followed as listed in both NFPA 13 and the Building/Fire Codes.   If those
> other requirements are met, even though that room may be unsprinklered, the
> intent of "throughout" is still met.
>
> There have been other cases where a substation of fire protection and
> prevention/control measures are required in lieu of sprinklers for a
> portion of a building.  The omission of sprinklers in the one portion did
> not render the building non-compliant with NFPA 8.1.1.
>
> If you have a unique condition it is best to seek opinion and acceptance
> of the AHJ and/or Owners' Underwriter/Risk Consultant.
>
>
>
> 8.1.1* The requirements for spacing, location, and position of sprinklers
> shall be based on the following principles:
> (1) Sprinklers shall be installed throughout the premises.
>
> A.8.1.1 This standard contemplates full sprinkler protection for all areas
> including walk-in
> coolers, freezers, bank vaults, and similar areas. Other NFPA standards
> that mandate sprinkler
> installation might not require sprinklers in certain areas. Based upon
> experience and testing,
> sprinklers have been found to be effective and necessary at heights in
> excess of 50 ft
> (15.2 m). For a building to meet the intended level of protection afforded
> by NFPA 13, sprinklers
> must not be omitted from such high ceiling spaces. The requirements of
> this standard
> should be used insofar as they are applicable. The authority having
> jurisdiction should be consulted
> in each case. A building is considered sprinklered throughout when
> protected in accordance
> with the requirements of this standard.
>
>
> Craig L. Prahl
> Fire Protection Group Lead
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29303
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Jamie Seidl
> Sent: Wednesday, August 20, 2014 8:34 AM
> To: [email protected]
> Subject: fully sprinklered definition
>
> I seem to remember that there was a paragraph in NFPA 13 that a building
> is considered fully sprinklered even when areas remain sprinklered where
> allowable by this standard.  Did I just dream this?  I can not find it this
> morning.
> Thanks,
> Jamie
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
     \ \