If it is in fact ductile iron, it is probably lined - at least I think so. If it is lines then the C-factor is probably supposed to be 140. Not very definitive, I know...
But who's to say there isn't something else wrong with the lead-in? Any chance of a partially shut valve somewhere? If I don't see anything posted, I may dig into this this weekend... Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | http://www.kfiengineers.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Travis Mack Sent: Friday, August 29, 2014 4:31 PM To: [email protected] Subject: Re: Modifications to C-Factor due to age of pipe This was not brought up in project specs or plans. Nor was it brought up in plan review. This was a project that had an existing 4" ductile supply line. It is supplying some paint booths and some exhaust ducts in an otherwise unsprinklered building. When the guys did the forward flow test of the new backflow preventer, there was an issue that they weren't getting as much water as they thought it should have. So, the EOR for the project comes back and says something about the calcs. According to my customer, the EOR says per a "chart" the C-Factor should have been 60 instead of 140. For 3 of the 4 paint booths, it is not a problem. They are small and plenty of margin. For the 4th, we end up with a problem. But, if there is nothing in the specs or criteria to cause the modification of that pipe, I am not sure where it will go. The good thing is that we still have a margin on the system, but it is less than the 10% required. I have just never heard of having to do this modification. I wanted to make sure it was something I have not been missing. Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected] On 8/29/2014 2:20 PM, Mark A. Sornsin, P.E. wrote: > Travis, > > Off-hand I can offer no help. > > But I am curious to see the responses. Had the engineer denoted the > requirement in the project drawings or specs, I'd definitely side with them. > If not, then I want to know if he has a leg to stand on (i.e. code reference). > > This CAN be a significant issue and is another example of a potentially > serious 'miss' by engineers who don't do their jobs with regards to sprinkler > system drawings/specs. E.g., take a 200 ft. run of existing 6 in. pipe - 50 > years old. They tell you to use it to modify the existing pipe schedule > sprinkler system to meet the new occupancy. Most often, a contractor can get > away with simply assuming it is 6" ductile with a c-factor of 140. But what > if in reality it is unlined cast iron? What C-factor are you to use? > > FM taught me that it depended on the water corrosiveness. Who determines > that? I don't know if the FM data is acquired from anything that could be > cited by code. Their tables say 50 yr old cast iron in mildly corrosive ware > should have a C-factor of 75; if corrosiveness is severe, it should be 40. At > an extra Hazard, Group I demand of 750 gpm, the friction though 100 feet of > pipe can vary from 1.5 psi at C=140; to 4.6 psi at C=75; to 14.9 psi at C=40. > Pretty significant variance and not something that should be blown off by > the engineer or designer. > > Ideally you'd do a water test THOUGH that pipe to verify actual friction > losses - but that is almost never a viable option. Then again, if you were > able to do so, you may be able to get a change order when you prove that the > engineer overlooked a serious issue. > > Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection > Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | > http://www.kfiengineers.com > > -----Original Message----- > From: Sprinklerforum > [mailto:[email protected]] On Behalf Of > Travis Mack > Sent: Friday, August 29, 2014 3:52 PM > To: [email protected] > Subject: Modifications to C-Factor due to age of pipe > > Does anyone know if there is any requirement in NFPA or Uniform Facilities > Criteria to modify the C-Factor of existing underground piping based on the > age of the pipe? If so, do you have a section reference so I can look it up. > An engineer is requiring us to do it, but won't provide the reference. > Yeah..It is one of those days. > > -- > Travis Mack, SET > MFP Design, LLC > 2508 E Lodgepole Drive > Gilbert, AZ 85298 > 480-505-9271 > fax: 866-430-6107 > email:[email protected] > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org > > ______________________________________________________________________ > This email has been scanned by the Symantec Email Security.cloud service. > For more information please visit http://www.symanteccloud.com > ______________________________________________________________________ > > ______________________________________________________________________ > This email has been scanned by the Symantec Email Security.cloud service. > For more information please visit http://www.symanteccloud.com > ______________________________________________________________________ > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org